this for the apprentices ,32 mcb on busbar 230volts no faults on kitchen ring circuit answers please .
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss what have got here in the UK Electrical Forum area at ElectriciansForums.net
no trick question . thats what I had to day.it had me stumped .the reason was it had a EICR done in 2016 .and missed that .Is this a trick question...
the blood screw at the bottom of the mcb ,that is was going round in circles and was not tighten up and a faulty S**ty BRITISH GENRAL MCB thats the second one I have changed over the last 2 years ,and not my customer .Missed what
So your first post should say volts and not faults.
was the busbar behind the cage clamp? seen that often.
no it was sat correct on the buzz bar , I put the screw driver to turn it to see if it was tight .and it half tight it was turning round and not biting. the brat just left it think it would be ok ,plus the last spark did a EICR on a up grade of the consumer unit and the test certs where photo copys .was the busbar behind the cage clamp? seen that often