spud1
Just processing an EICR and noticed a couple of final circuits measured Zs values (fed from a sub distribution board) slightly exceed the Max permitted Zs values for the OCPDs that protect them.
Obviously I will note this as a design flaw in the observations, but I just wondered, from the perspective of ADS, as the circuits are also protected by a 30Ma RCD, does this negate the need to fully consider Maximum permitted Zs values for the OCPDs?
Is it not deemed that the fault protection in this event could be being provided by the RCD?
After all, if the earthing system was TT the measured Zs values would be way higher than the Max permitted for the devices...
Cheers
Spud.
its poor design to not achieve the Zs for the protective device when installing but sometimes it can not be avoided which is where the rcd comes in as for a 30mA the max Zs is 1667 ohms. Its not often I come across a circuit with the Zs for the mcb and circuit being outside that allowed but the RCD does provide a get out clause
So how would you report on it in the EICR, if at all?
FI if it is not possible to carry out investigation there and then. personally I would not code it as whilst its not an ideal design the regulations - although i cant recall it word for word does permit the use of rcd for fault protection when the circuit Zs is too high for the circuit protective device rather than additional protection.
If the Ze is a decent reading and there is no external reason the Zs should be higher than the max permitted then it is a non-compliant install as the RCD should be for additional protection not fault protection.
As this is a periodic and RCDs are installed I would only code this as a C3 as the RCD is providing fault protection so there is no immediate danger but the installation is not to BS 7671. I would clarify within notes on the report.
If the Ze is high and the high Zs could not be avoided then no code as it is acceptable to use an RCD as fault protection in this instance.
When you say, "slightly exceed," was the circuit designed prior to the introduction of the Cmin fudge-factor, and would it have complied at the time of design? Not that it really should influence your decision on coding as you're comparing the results to those required by the current edition of BS7671, but it might explain it. Sounds like poor design though, anyway.
Yes very possibly complied at the time of install. Probably installed in late 15th maybe early 16th edition. Readings are within 0.10 ohms of compliance with current standards
spud1
Somerset
What if a circuits Max Zs is exceeded but the circuit is protected by an RCD?
spud1,
Bobster,