Deleted member 123470

Hi,

I'm currently installing a new consumer unit and I cannot clearly identify my earthing arrangement.

(image attached)

I am leaning towards TN-S but could potentially be TN-C-S as it is a unit installed in the 70's and doesn't match the drawings in the OSG. Any expert advice would greatly appreciated.
 

Attachments

  • DSC_0503.JPG
    DSC_0503.JPG
    75.1 KB · Views: 118
Don’t think it’s a tns

Have you done a Ze at the old fusebox by any chance ?
 
Is that black lead apparently coming from the lower left of the head an earthing conductor?
Yes it is, it feeds directly into a MET then to the current consumer unit.
[automerge]1572685823[/automerge]
Don’t think it’s a tns

Have you done a Ze at the old fusebox by any chance ?
Not yet, will be the first thing I do before replacing the CU to make sure it's within 0.35 ohms. Just trying to determine the arrangement before doing the paperwork so I can challenge the supplier if their is a problem. Its a very old system an falling to bits
 
Last edited by a moderator:
my bet is that it's sweated onto the incoming cable sheath, under that plastic below the fuse.. therefore TN-S.
 
my bet is that it's sweated onto the incoming cable sheath, under that plastic below the fuse.. therefore TN-S.
That's what I was thinking, cheers. I think I'm going to ring the supplier just to be certain.

Tganks
 
Test pefc and pssc and compare results ?

Your profile lists you as a diyer which is very concerning.
I'm Part P qualified and have a lot of experience with basic electrical work. so have the necessary knowledge to make these upgrades. DIYer was the best fit option. Just got caught off guard by this old cut out. Appreciate the concern buddy
 
I'm Part P qualified and have a lot of experience with basic electrical work. so have the necessary knowledge to make these upgrades. DIYer was the best fit option. Just got caught off guard by this old cut out. Appreciate the concern buddy
maybe you should edit your profile. if you've done a short course and joined a scheme, then Domestic Installer would be appropriate. If you don't have that option, I'm sure Dan could make it happen.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
What is my Earthing Arrangement?
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
14

Thread Tags

Advert

Thread statistics

Created
Deleted member 123470,
Last reply from
Baddegg,
Replies
14
Views
2,477

Advert

Back
Top