S
sivoodoo
Hi all,
I had a call yesterday from a friend who is living in rented accommadation.
He has just moved in last week. No PIR had been done and no paperwork at the CU.
He called to tell me the power to the whole house has gone.
On ariving I found that a wine bottle cork had been taped to the main switch on the consumer unit (i would imagine to keep it from flicking off) and that the 25mm neutral tail had burned out.
I removed the main switch (100 amp square D) and found that it has melted and no continuity through the neutral. It appears that the neutral tail had not been tightend properly or come loose.
I did not have a Square D 100 amp main switch on me at the time so replaced it with an MK main switch 100A. The fittings are identical.
Also I found that the main cut out was in a bad state. 1930s asbestos fuses, fused neutral and loose fuses, no seals on the box, very frayed 10mm tails from cut out to meter. I called YEDL who came out and replaced the cut out and tails promptly.
My question is what tests should be carried out? I am Part P registerd and am happy to carry out the tests but was wondering what test would be required. Would this be considerd replacement like for like or will swapping the main switch require full certification.
any help much appreciated.
I had a call yesterday from a friend who is living in rented accommadation.
He has just moved in last week. No PIR had been done and no paperwork at the CU.
He called to tell me the power to the whole house has gone.
On ariving I found that a wine bottle cork had been taped to the main switch on the consumer unit (i would imagine to keep it from flicking off) and that the 25mm neutral tail had burned out.
I removed the main switch (100 amp square D) and found that it has melted and no continuity through the neutral. It appears that the neutral tail had not been tightend properly or come loose.
I did not have a Square D 100 amp main switch on me at the time so replaced it with an MK main switch 100A. The fittings are identical.
Also I found that the main cut out was in a bad state. 1930s asbestos fuses, fused neutral and loose fuses, no seals on the box, very frayed 10mm tails from cut out to meter. I called YEDL who came out and replaced the cut out and tails promptly.
My question is what tests should be carried out? I am Part P registerd and am happy to carry out the tests but was wondering what test would be required. Would this be considerd replacement like for like or will swapping the main switch require full certification.
any help much appreciated.