Thought i would start with one i had 30 years ago!
Office block, loads of fluorescent's etc all the ground floor not working, rewireable fuse.
Fuse wire disintegrated so fault not overload.
Meggered everything, clear L-E, N-E. but picking up control gear for L-N.
Thought i would try just putting new fuse wire in! Tried it and everything worked OK.
Three weeks later same call.
Thought i better do it properly this time so took down all flo's, checked gear inside, disconnected gear. Meggered again, no fault apart from L-N.
Checked with staff to see if any other rooms. Oh yes , a store cupboard.
Found an enclosed light fitting with 100 W lamp in it. It was the sort with the aluminium "pie dish" reflector. I found that it had chock block connectors behind it that had half melted to the earthed pie dish.
Turns out they hardly use the store cupboard and if someone left light on for more than 15 minuets the chock block would get hot, melt against pie dish and blow fuse, then as it cooled the plastic would retract and hey presto no fault!
Office block, loads of fluorescent's etc all the ground floor not working, rewireable fuse.
Fuse wire disintegrated so fault not overload.
Meggered everything, clear L-E, N-E. but picking up control gear for L-N.
Thought i would try just putting new fuse wire in! Tried it and everything worked OK.
Three weeks later same call.
Thought i better do it properly this time so took down all flo's, checked gear inside, disconnected gear. Meggered again, no fault apart from L-N.
Checked with staff to see if any other rooms. Oh yes , a store cupboard.
Found an enclosed light fitting with 100 W lamp in it. It was the sort with the aluminium "pie dish" reflector. I found that it had chock block connectors behind it that had half melted to the earthed pie dish.
Turns out they hardly use the store cupboard and if someone left light on for more than 15 minuets the chock block would get hot, melt against pie dish and blow fuse, then as it cooled the plastic would retract and hey presto no fault!