Your later post states that the incomer is bottom right. It's not really clear what the intention of this circuit is - possibly straight out to the centre SWA (with no isolation), via switch to the larger diameter left hand SWA, and also via the meter to the 2x13A sockets?
So, roughly in order of my perceived seriousness (please comment!)
1. Exposed live terminals (L and N) on the switch (which we will come back to later).
2. No continuity of Earth.
3. (Related to 2) incorrect termination of SWA, particularly the armour - should be glanded. On two of the SWAs, not glanded/terminated at all, on the third it is incorrectly terminated to an earthing terminal, to which there are no other connections.
4. No means of isolation for a circuit that is clearly intended to be able to be isolated, as switch is bypassed.
5. 13A sockets not RCD protected (outside)
6. Inappropriate materials for 2x13A sockets (rusted, so not intended for use in this environment).
7. Assuming this is accessible to unskilled/unsupervised persons, single insulated cables should not be used (ends of the SWA, the ends of the T&E, and most likely all that red cable too).
8. Is that board alright? Looks like chipboard that's decomposing, does it have enough mechanical integrity to support the cables and fixtures? (I assume so as you've re-used it!)
9. Incorrect colour cable used for neutral (red instead of black).
EDIT: 9b. Cables should be clipped/supported.
10. Incorrect clips used on red cable going into bottom of (bypassed) switch.
Unclear if the SWA on the ground (yellow tape on one end) is an off-cut or is in some way connected...
Cheers for posting this