OK sorry I'm being really impatient and possibly thick here, but I've just done this for the first time today .....


if a switchfuse is used on tails over 3m long to protect the DNO fuse, should the fuse rating in the switchfuse be less than the DNO main fuse? If not why not? I think I'm missing the point here??????
 
On industrial it is often the case (example) that say DNO have 200Amps and busbar main isolator for instance might be the same but if you reference the type that DNO use they tend to give allowance i.e. type 3, 4 or 5 against your bs88 type 2 this give your fuses priority, where as some commercial and domestic use standard type 2 DNO fuses and even with reduction of your fuse size in the case of a short circuit full discrimination wont be achieved anyway only partial in some cases..... its usually accepted that domestic cannot achieve full discrim' but to check if 2 fuses up and downstream of each other give full discrimination then check that the total let through energy (I^2t) of the downstream device is less than the pre-arcing energy (I^2t) of the upstream device.... if so then you have acheived full discrim'

Example if you have a bs88 63amp fuse Gg1 it will only achieve full discrimination to a 6amp (b) mcb, 10amp - 40amp will give partial discrim' decreasing respectively as your mcb rating increases but no discrim will be acheive between bs88 63amp and a 50amp and obviously a 63amp mcb type b.

Hope you can appreciate now how hard it is to get full discrimination on short circuit and as my example shows if your front end is a bs88 Gg1 63amp fuse then anything above 6amp (b) mcb wont acheive full discrim'.

Discrimination for overload current is an easier thing to understand and meeting full discrim' in this case isn't rocket science so wont bother explaining that one ;)

............
Ill just add to this (edit)... when discriminating against overload my comment just then is in ref' to similar devices but if you are comparing 2 differing divices a trick is to print the time current curve of one device on paper the the second device on tracing paper and overlay to see what needs to be done to achieve discrim' under overload condition as sourcing comparison charts cn be a pain.

re' short circuit discrim', Hagar's fuseboards catalogue has a tech' section that will compare in chart form different devices from bs88 to mccb's etc etc very helpful reference an im sure you'll be able to get it online.
 
Last edited by a moderator:
well...on the basis that an avarage sized house...2-3 beds....may get up to what?...say 60-65A at max demand times....5-7 PM ish....i reckon a 60A will hold nicely for the duration of max demand at least....so if this sounds like its about right for the scenario you have posted about.....
 

Reply to What Should Rating of Switchfuse Be? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
841

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
487
sounds like one of those jobs to swerve and let it be someone else's problem
Replies
12
Views
923

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top