No No Design current equals 1000 x kva divide it by square root 3 x line to neutral voltage.

So that's 75000 divide by 1.72 x 400

75000 / 688 = 109 amps

Grouping factor is 0.79 as there will be 3x 3phase circuits grouped together touching each other.

There is no ambient temperature factor as temperature will be aboutn room temperature and no insulation factor as it will be clipped direct to wall.

It will be protected by bs88 fuses, 1.25 fuse factor


Design current / factors
109amp/0.79x1.25= 110.37 amps

Volt drop can be only 5% of supply voltage for all except lighting which is 3%. So for 400v max volt drop 20volts.

Looking at table 4e4a I will need 25mm cable.


Volt drop for 25mm 3/4 core swa is 0.14 mv/a/m

I estimated about 30metres length so 30x110.37x0.14 = 463.55

463.55/ 1000 = 0.463 volts.

So that's well within the permitted volt drop.

I can't work out shock protection as I don't have ze value.

This guy is a menace! He needs physically stopping! He's going to kill someone one day!

electricshock, you are contravening BS 7671 by carrying on what you are doing without being competent to do so. You are also breaking the law as you are contravening The Electricity at Work Regulations 1989; regulation 16.

Stop what you are doing before you hurt someone and get a competent electrician to do the work, as you are not!

I for one cannot believe how so many people on here have helped this fella on his merry way, let alone been civil! I'm all for helping people to a certain extent, but this guy needs an education!!!

Calm down. I've connected dozens of machines without any problems.
 
Is it possible if someone can check if my calculations are right. Anything I missed. Let's just pretend I'm in class.

Seriously matey, jog on.

Anyone willing to help you go out and potentially kill someone is a fool!

Calm down. I've connected dozens of machines without any problems.

I have seen the result of sparks who snip cpcs at class 1 accessories without any problems! I have seen plenty of builders have a go at electrical work themselves without any problems! I have seen the result of 5WWs playing around with three phase gear that they don't understand without any problems!

You see where I'm going fella?!

One day there will be a problem, and it'll be you hauled up in front of a jury to defend yourself on a corporate manslaughter charge!
 
Please explain how I will potentially kill someone. According to my calcs what is wrong. At the moment I'm just working on 75kva total power. I'm gonna get full details soon.
 
Please explain how I will potentially kill someone. According to my calcs what is wrong. At the moment I'm just working on 75kva total power. I'm gonna get full details soon.

Because you don't know what you are doing! The very fact that you came on here asking what to do in the first place was proof enough!

You are breaking the law if you carry out this work unsupervised, end of!
 
Is the machine new or old?
Is the motor DOL, Star/delta, VSD, soft started ?
Is their a long run up time?.... been a drill its doubtful?
Have you calculated supply demand before this machine is fitted (is the existing supply to premises able to cope)?
What is the operational duty of the machine (starting , stopping inching if it has one?)

Seriously i could go on and on and whats the point of spoon feeding you questions if when given the answers you still wouldn't know what they may mean or entail, any one of these questions could have an effect on the cable sizing ....if indeed the 22kw is the main motor where is the rest of the power going approx 60amp per phase .... you have a machine spec' but it probably gives you little info except the supply required... You need to talk to the manufacturers and ask them the correct questions... caution note if you sound like you haven't a clue what your doing i can guarantee they will just say to your customer what can of muppet you got wiring our machine in!...

The machine specs you have supplied don't exactly tally and need confirming why you have 2 values (75Kva and 22kw)... i can teach a monkey to do cable calcs in a day -trust me ive had to do it often enough but it would take yrs in an Industrial environment before i believe someone is ready to spec' machine supplies?
 
might have been a better idea to try and find a spark experienced in this type of work and split the job. you both earn and you learn. customer gets his machine going. everyone's a winner.
 

Reply to What size cable do I need? in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
618
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
776
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Question
Well another week passed and I still don't have a proper answer to where the process is wrong. To reiterate, this is not a question for a real...
Replies
2
Views
203
No table I just know the conductivity of the armour is around 4.0mm² copper equivalent so 6.0mm² will be fine.
Replies
6
Views
423

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top