So im a third year apprentice and should be qualified next year (whoopee). One thing has always made me curious and that is what cable size should we be using to rewire or in a new build for lighting in 2021? OF COURSE this depends on the load and how it's installed etc but in general what size cable would you use?
Out of the three people I worked with only one of them used 1mm. I kind of levitate towards that side as well and I'll explain why right now -
1mm cable can handle 8amps when surrounded all sides with thick insulation. That's 8x230 so 1804 Watts. 16amps clipped direct, that's 3680 watts. If anything we are all gonna be seeing more and more LED's with low power consumption and even if we don't... Well we could still have 26, 70 watt bulbs in one circuit if the cable is surrounded in insulation... Which it rarely is. Usually it's ran on top of the insulation anyway. That doubles too 52 when clipped direct! I know the price difference isn't that much but it all adds up.
I would love to know the cable size you qualified electricians use and maybe if you have time a little comment explaining why. Like I said I should be qualified next year and want to evaluate everyone's opinions before I go ahead and make my own decisions in the future.
 
1mm in a small domestic property. Easier to terminate and never seen thermal damage due to insulation. Installations should be designed to use materials without waste so 1.5mm in this scenario is wasteful in my opinion. Some will no doubt disagree ;)
Totally agree with ImpededLoop.
I've never seen thermal damage due to insulation either.
 
With LED lights it would have to be a massive house to reach the VD limit.

Yes, you might get to the Zs limit of a MCB and I'm not very keen on relying on the RCD part to meet disconnection, but for your typical 6A B-curve it is quite a lot (don't have OSG to hand to check but will look it up later).

Hmm, an RFC for lights in 1mm....
 
With LED lights it would have to be a massive house to reach the VD limit.

Yes, you might get to the Zs limit of a MCB and I'm not very keen on relying on the RCD part to meet disconnection, but for your typical 6A B-curve it is quite a lot (don't have OSG to hand to check but will look it up later).

Hmm, an RFC for lights in 1mm....
Nah...

Combined lighting and power circuits on 16a breakers all in 1.5
 
I would love for someone to make a case for 1.5mm cable as I have post this on a few places and haven't had anyone really make a good case for using 1.5 other than futureproofing.
Maybe it's inevitable that I will be using 1mm when Its my decision :) of course I will be mindful of all necessary factors though.
Thanks everyone who took the time too look things up and comment on this post. Really love that I came across this website.
 
I would love for someone to make a case for 1.5mm cable as I have post this on a few places and haven't had anyone really make a good case for using 1.5 other than futureproofing.
Maybe it's inevitable that I will be using 1mm when Its my decision :) of course I will be mindful of all necessary factors though.
Thanks everyone who took the time too look things up and comment on this post. Really love that I came across this website.
The only people that I have ever known to make a case for 1.5 have been “electricians” who say all lighting is done in 1.5 it’s the way I was shown and it is the only way.
 
I would love for someone to make a case for 1.5mm cable as I have post this on a few places and haven't had anyone really make a good case for using 1.5 other than futureproofing.
Maybe it's inevitable that I will be using 1mm when Its my decision :) of course I will be mindful of all necessary factors though.
Thanks everyone who took the time too look things up and comment on this post. Really love that I came across this website.

Ok here is one, I work both domestic and commercial, I often find commercial with 10A lighting circuits (Also see it in domestic) With more and more people piling more and more insulation into their lofts the derating factor of 0.5 could be achieved that would take it below 10A. Because of this I use 1.5mm when dealing with circuits with 10A lighting just to be safe..

Having said the bullc**p above which 1mm would be fine for most scenarios, here is the two real reasons I only use 1.5mm..

1. I don't have the space to carry around 1mm and 1.5mm T+E as well as 1mm 3core and earth and 1.5mm 3core and earth and then there is singles... so I just carry 1.5mm
2. I find 1.5mm is more resilient in a terminal, have a number of times with 1mm when you do the tug test the copper breaks because of the intents from possibly being over tightened. I don't seem to get this issue with 1.5mm

maybe if copper prices keep going up then I might change my mind but for now mainly really for space and the advantage that I don't have as much stock which is more efficient. The cost difference between 1mm and 1.5mm is not yet enough that I would bother carrying both..

Also although its seems like 68m is a long distance its surprising on a larger house how it can start to get close, 1.5mm you don't have to think about it, its also really difficult to judge how long the run is (Probably me being lazy though)... Would not dis anyone for using 1mm for lighting its just personal preference for the 2 above reasons why I use 1.5mm
 
If looking at 10A of lighting in some methods then yes 1.5mm makes sense and it is physically stronger.

But I would be astonished to see that load level in any domestic house with LED lights. You would expect to see different floors of any multi-storey building on separate circuits just to reduce the impact of a fault taking out ALL lights, so really 6A is more than enough unless its a massive hotel-size floor, etc (for LED at ~3A total that is equivalent to about 4kW of old filament lamps so about 40 traditional 100W points, say 15 rooms with two lights and a corridor with 10?).
 

Reply to What size cable do you use for new lighting circuits? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Well another week passed and I still don't have a proper answer to where the process is wrong. To reiterate, this is not a question for a real...
Replies
2
Views
126

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top