I thought it would fail an inspection because the system is being upscaled from source (16 to 32 or even 63a) and it could be accidentally overloaded by an untrained or ignorant user.

The system is not being 'upscaled' nor is it being exposed to any more potential for overload than if the adaptor was not used.

It will not fail an inspection as there is nothing dangerous, potentially dangerous nor even remotely questionable or unusual about it.
The entire theatre and events industry would be royally screwed if such adaptors were not permitted or safe!

A 16A supply will have overload protection at 16A, regardless of what you plug in to it.

It is adaptors which go the other way without using an appropriate fuse or circuit breaker which are dangerous. For example a commonly found adaptor which is dangerous is the 32A plug with two 16A sockets connected directly to it.

The simple rule is that you can have an adaptor with a socket of a larger rating than the plug, but you cannot have an adaptor with a socket of a smaller rating than the plug without additional fusing.


How on earth are you managing to comply with BS7909 if you don't even understand this basic principle? Or are you another one of those people who ignore BS7909 completely and earn the whole of our industry a bad reputation?
 
Last edited by a moderator:
The system is not being 'upscaled' nor is it being exposed to any more potential for overload than if the adaptor was not used.

It will not fail an inspection as there is nothing dangerous, potentially dangerous nor even remotely questionable or unusual about it.
The entire theatre and events industry would be royally screwed if such adaptors were not permitted or safe!

A 16A supply will have overload protection at 16A, regardless of what you plug in to it.

It is adaptors which go the other way without using an appropriate fuse or circuit breaker which are dangerous. For example a commonly found adaptor which is dangerous is the 32A plug with two 16A sockets connected directly to it.

The simple rule is that you can have an adaptor with a socket of a larger rating than the plug, but you cannot have an adaptor with a socket of a smaller rating than the plug without additional fusing.


How on earth are you managing to comply with BS7909 if you don't even understand this basic principle? Or are you another one of those people who ignore BS7909 completely and earn the whole of our industry a bad reputation?

The amount of people who don't even have a grasp of Bs7909 is scary


Sent from my iPhone using Tapatalk
 

Reply to What size supply? in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Adding a led strip isn't going to make much difference to the 3 phase balance. No real difference to where a 3 phase machine uses one phase to...
Replies
2
Views
360
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
514

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top