I can't remember his name, but I'm pretty sure it wasn't David Turpin
Ok, thanks, we will see what he thinks about it tomorrow as it will be obvious from my certs I haven't been doing a Zs on a radials........
To be honest, I find it hard to belive folks don't carry out Zs testing. And I certainly would be doing it for my assesment, in fact that was the test I had to carry out for Elecsa this year!
Well, my Elecsa assessment is done (passed without any problems ;) ) and I asked the guy about this. He confirmed that they like to see a Zs test to back up the dead tests. He did agree though that could be see as contrary to the EWR (minimising live testing) so should only be done if there was safe access to the live circuit.
I too was asked to do a Zs on a radial circuit for the assessment.
Reply to what tests are you doing on consumer unit change. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
    • Friendly
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...