The test is carried out between live conductors, ie phase and neutral, connected together, and the body of the appliance.. (quote from guide)


page 75 in service inspect and test table 15.2 gives the readings which for class II is 2.0Mohms.


Hope that helps




Chris
 
Last edited by a moderator:
Hello acat,

So would you think in the case of a charger, do we do 500v ins res put the probe on the casing and dont do any other test , load etc because I cant connect the phone to the charger and test , becuase it may damage the equipment.

Thanks
 
In the case of a class I or class II appliance the body of the appliance woulld need to have exposed metal parts for an insulation test to be carried out.
Might be wrong but I think the minimum IR for a class I is 2 megohms and 7 megohms for a class II.

Hello acat,

So would you think in the case of a charger, do we do 500v ins res put the probe on the casing and dont do any other test , load etc because I cant connect the phone to the charger and test , becuase it may damage the equipment.

Thanks

So you are going to put the probe on an all insulated plastic case ???:confused::confused::confused:
 
Last edited by a moderator:
Page 75/76 of the guideexplains the tests and if you look at table 7.1 on page 34 it gives a scedule for formal visual inspection and a second row for combined inspection and testing for class II equipment its only in hotels offices and shops where no testing takes place.



Chris
 
In the case of a class I or class II appliance the body of the appliance woulld need to have exposed metal parts for an insulation test to be carried out.
Might be wrong but I think the minimum IR for a class I is 2 megohms and 7 megohms for a class II.



So you are going to put the probe on an all insulated plastic case ???:confused::confused::confused:

I'm with you on this one wirepuller. If the plastic case has exposed screwheads that go into the body of the appliance then you may be able to connect these to the earth probe but if the appliance is totally plastic with no exposed conductive parts at all then you can't do the test. And, unless the casing is cracked or chipped in some way, which you would pick up on a visual inspection, then no exposed conductive parts should mean no risk of electric shock.
 
Last edited by a moderator:
You cant test items like phone chargers and phone cradles....there is nothing to test as they are class 2 with no exposed metal parts.....a visual inspection only is appropriate.

Am I the only one with 2377 around here? Phone chargers are class III and you can only do an insulation test at 250v but even then I wouldn't, chance of damaging the electronic transformer. I'd just inspect it, then function test and pass it.
 
Am I the only one with 2377 around here? Phone chargers are class III and you can only do an insulation test at 250v but even then I wouldn't, chance of damaging the electronic transformer. I'd just inspect it, then function test and pass it.

If a phone charger plugs into a 230V mains supply then it cannot be class III.
It would be the equipment that connects to the charger itself that is class III.

Personally I wouldnt bother tessting anything that runs on <12V, because even if it was broken would not offer risk of electric shock.
It would be like condeming a 9V battery for having exposed conductors :D
 
As xraytek states phone chargers are class II.....have a look at yours and you will see the small square within a larger square symbol which denotes a double insulated class II appliance.
 
I always test AC/DC adaptors such as mobile phone chargers.

I never test the appliance at the other end if it is just a battery powered appliance for two reasons,

its going to be SELV (less that 50V, and usually 5-12 volts) so its safe as far as an electric shock hazard is concerned, and secondly it is going to contain very sensitive micro-electronics.

With regards to testing the adaptor itself, the most important thing in my mind is the visual, you still have 230V going into the adaptor so if the case is cracked, or the case cover is missing, there is a huge risk there.

The other test i would do is the Insualation Resistance test.

I always label the phone charger, but never the appliance attached to it. Thats just penny pinching :(
 
Whether phone chargers are class 2 or three doing a 250V test will do no damage ( unles the transformer could be 110V). I PAT test for charity shops at £1.00 an item ( that is for charity organisation and the items are sold to the public, I also repair if possible but throw most repairable items away). We get many phones at the various shops and it is just the charger that is tested and operational test, does the phone charge.. Same with PS2 and the lkes that come in. Test the lead for insulation and full operational test of the PS2. It depends on how thorough you wantto be and how quickly you want to earn money, and how thoroughly you understand the practicalities of electrical appliances
 

Reply to What to PAT test in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
800
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
982

Similar threads

what is the piece of equipment and part number?
Replies
9
Views
720
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top