Hello all..

I expect my full rewire will be assessed this year by Stroma.

It has been done very well and neatly and ticks all the regulation boxes..... apart from socket/switches heights. These I have kept as existing, approx 1350mm for switches and 300mm for sockets.

I have rang Stroma and they have said that a full rewire needs to meet Part M requirements for these heights. I realise BS7671 553.1.6 doesn't give these heights but Part M does and if Stroma say it has to be then there's no arguing really. Also, even though the vast majority of threads say that a rewire does not need to meet part M heights I believe it does as Section 0, 0.2 says part M applies to new builds and also 'Material alterations' of existing dwellings.

Basically my question is 'could they possible make me change all the heights'? I can't believe they would as that's crazy, but just looking for reassurance. I expect it will go down as a note and be checked for the following year to make sure I have adhered to the heights?
 
Last edited:
Well, what happens in the scenario a rewire where the customer does not want chasing of walls you are doing like for like rewire. If you had to do surface ie mini trunking you would be left with the old boxes at the old hights if you were to do Part M.
 
Thats not quite true as I'm aware. The Documents apply to all building work, with some exemptions.

Part M would not apply to an alteration or extension to an existing dwelling. However, as I and others have already suggested a major refurbishment of a dwelling, e.g. completely renovated for example, requiring structural change, then Part M and others may be applied. There are 'limits on application'.

To say it applies only to new builds, is not quite correct IMO. Sorry if I'm being picky.

I think we are all agreed that in this instance a rewire does not constitute material alteration. But HHD will need to discuss this with his scheme. Its his assessment with them.

I just took it directly from the Part P document.

3EAFFB21-31E6-4585-8E83-6B79277E836C.jpeg
 
Last edited by a moderator:
In recent years I've used several rewires for my annual assessments with Stroma now non of which were questioned over the socket and switch heights. The only times I've complied with Part M regarding socket and switch heights is on new builds and properties which have been gutted back to brick inside and likely to be used by disabled persons i.e. ground floor flats, bungalows etc. I shouldn't worry about it unless of course your assessor turns up in a wheelchair.
 
I just took it directly from the Part P document.


I sorter stand corrected. The definition of material change (reg 5), gives 10 examples.

From the online Doc M;
Meaning of material change of use (reg 5), i) the building contains one room for residential purposes, contains a greater or lessor number of such rooms, than it previously did.
I think thats describing alteration or extension?

However, Requirements relating to material change of use (reg 6), does not list i), only change to hotels, institutions etc for application of M1 (access & use).

So give agree with you there.

But then the document bumbles around with not making it less compliant than it previously was or reduction, which I can't decipher! Which was my point really, that Doc M still can apply to an alteration or extension. I still agree that a rewire doesn't constitute a material change of use.
 
Meaning of material change of use
I think thats describing alteration or extension?
No. change of use specifically means it had one use ie retail or commercial and then became residential. It wouldn't be change of use if you changed the use of a garden into a room!
not making it less compliant than it previously was or reduction, which I can't decipher!
That just means if the sockets are at 300mm you can't lower them but you can keep them at 300mm or higher.
 
I was recently on a job where an agricultural building which had been in use as a brewery and is now being converted to a dwelling was being wired for its new use as a dwelling. There was a freelance building inspector on site and I specifically asked him if Part M applied and he said no, put the accessories at whatever height the customer wants. I'm with Stroma too but probably won't be taking them to this one on assessment...!
 
No. change of use specifically means it had one use ie retail or commercial and then became residential. It wouldn't be change of use if you changed the use of a garden into a room!

That just means if the sockets are at 300mm you can't lower them but you can keep them at 300mm or higher.

Your first point, if you read item I) in below, and explain for me?

Screenshot (3).png

Your second point, its item 0.4 thats a bit gobbledygook.
 
I haven't the reference to back it up, but I would have thought that brewery to a dwelling job would definitely have triggered the new build clauses for outlet and switch heights. If it didn't (as that inspector says) then is he also saying he doesn't need to see the latest domestic insulation or smoke alarm standards? Just to make a point :) .
 
I don't understand what has gone wrong?
I put some impromptu pictures of the install up and no one has said anything bad or picky???
This is not normal behaviour and I feel quite left out.... almost abandoned:(! For heavens sake chaps I'm a Electrical Trainee (well, 6mw)... where's all the bashing!!!
However, I can understand it if you all feel that I'm perfect :D

(PS.. no response from Stroma yet to my email.
 
I don't understand what has gone wrong?
I put some impromptu pictures of the install up and no one has said anything bad or picky???
This is not normal behaviour and I feel quite left out.... almost abandoned:(! For heavens sake chaps I'm a Electrical Trainee (well, 6mw)... where's all the bashing!!!
However, I can understand it if you all feel that I'm perfect :D

(PS.. no response from Stroma yet to my email.

They're all too busy bumping their gums about how to earth a back box. :)
 
Your first point, if you read item I) in below, and explain for me?

View attachment 43872

Your second point, its item 0.4 thats a bit gobbledygook.
Midwest very sorry about the delay I was away and didn't have time before leaving to open up the laptop and gather all the references. Normally I access the forum on my mobile phone. I hope it will be worth the delay!

I've looked at the online version so I could get the context of the previous page, and I think it's changed from your version.
https://assets.publishing.service.g...BR_PDF_AD_M1_2015_with_2016_amendments_V3.pdf
Using the new document, it's quite specific in the guidance now:
upload_2018-8-26_20-42-4.png

Looking at the actual regulation 5 in the legislation it does match your quote, but the context is essential here (see underline): The Building Regulations 2010 - http://www.legislation.gov.uk/uksi/2010/2214/regulation/5
"there is a material change of use where there is a change in the purposes for which or the circumstances in which a building is used, so that after that change... ...the building, which contains at least one room for residential purposes, contains a greater or lesser number of such rooms than it did previously"
So it specifically only includes changes in what you're using the existing building, rather than changes resulting from building work.
Also the regulation itself excludes extensions specifically
upload_2018-8-26_21-14-17.png



Regarding 0.4, again it's changed in the latest version to 0.11
upload_2018-8-26_20-48-39.png

Looking at regulation 3 The Building Regulations 2010 - http://www.legislation.gov.uk/uksi/2010/2214/regulation/3
"
(2) An alteration is material for the purposes of these Regulations if the work, or any part of it, would at any stage result—

(a)in a building or controlled service or fitting not complying with a relevant requirement where previously it did; or

(b)in a building or controlled service or fitting which before the work commenced did not comply with a relevant requirement, being more unsatisfactory in relation to such a requirement.
"
So a socket at 300mm doesn't comply, but it would be a material alteration if you moved it down to 200mm. Adding further sockets at an existing non compliant height, to me (non professional) would be a material alteration. However part M above specifically says that the building overall shouldn't be less compliant, so that clarifies matters somewhat.

Let me know if that is unclear - it's certainly clarified my understanding somewhat!:)
 
Last edited:
Just want to throw in a curved ball ... What about above counter sockets in kitchens .... They would struggle to comply with part m
Most kitchen sockets are within the appropriate range for habitable rooms (inc kitchens) in visitable dwellings for people with reduced mobility.
I suppose you don't consider that sockets at 1200 with a 600 depth unit in front meet the performance suggestion:
upload_2018-8-26_21-10-2.png

Thinking of older people I know, I think bending tends to be the tricky part rather than reaching forward, so perhaps the requirement isn't as far off as we'd expect?

Interestingly, for houses for people in wheelchairs, the requirements are far more strict and the whole kitchen is built around suitable requirements. The relevant part would be
upload_2018-8-26_21-7-0.png

I would expect the layout would be designed and provided by a designer for all the trades in that situation though.

upload_2018-8-26_21-9-36.png


upload_2018-8-26_21-9-39.png
 
Let me know if that is unclear - it's certainly clarified my understanding somewhat!:)

I really don’t understand what you are doing on here John, but what I do know is that the building regs are far too open to interpretation so my advice stands to the op

If Stroma think it’s wrong, ask them to clarify in writing what Is wrong and why

But go ahead with the assessment as I would wager a large bet it won’t be raised.
 
Midwest very sorry about the delay I was away and didn't have time before leaving to open up the laptop and gather all the references. Normally I access the forum on my mobile phone. I hope it will be worth the delay!

I've looked at the online version so I could get the context of the previous page, and I think it's changed from your version.
https://assets.publishing.service.g...BR_PDF_AD_M1_2015_with_2016_amendments_V3.pdf
Using the new document, it's quite specific in the guidance now:
View attachment 43910
Looking at the actual regulation 5 in the legislation it does match your quote, but the context is essential here (see underline): The Building Regulations 2010 - http://www.legislation.gov.uk/uksi/2010/2214/regulation/5
"there is a material change of use where there is a change in the purposes for which or the circumstances in which a building is used, so that after that change... ...the building, which contains at least one room for residential purposes, contains a greater or lesser number of such rooms than it did previously"
So it specifically only includes changes in what you're using the existing building, rather than changes resulting from building work.
Also the regulation itself excludes extensions specifically
View attachment 43916


Regarding 0.4, again it's changed in the latest version to 0.11
View attachment 43911
Looking at regulation 3 The Building Regulations 2010 - http://www.legislation.gov.uk/uksi/2010/2214/regulation/3
"
(2) An alteration is material for the purposes of these Regulations if the work, or any part of it, would at any stage result—

(a)in a building or controlled service or fitting not complying with a relevant requirement where previously it did; or

(b)in a building or controlled service or fitting which before the work commenced did not comply with a relevant requirement, being more unsatisfactory in relation to such a requirement.
"
So a socket at 300mm doesn't comply, but it would be a material alteration if you moved it down to 200mm. Adding further sockets at an existing non compliant height, to me (non professional) would be a material alteration. However part M above specifically says that the building overall shouldn't be less compliant, so that clarifies matters somewhat.

Let me know if that is unclear - it's certainly clarified my understanding somewhat!:)

Thanks for the reply & time.

I can't find that the definition of material change of use, has been altered (or removed) in the latest legislation (Reg 5; (i) the building, which contains at least one room for residential purposes, contains a greater or lesser number of such rooms than it did previously. Clearly relates to an extension or alteration of a building. However, Reg 6 Requirements relating to material change of use, does not list Reg 5 (i), to include M1.

So in the broad sense, an alteration or extension to an existing property, is a material alteration, but not all the Documents apply, including M1. Not commenting on Reg 3, so as not to confuse things!

However, the Guidance given in 0.4, is what appears to meander around IMO, although it does give one example of removing a downstairs toilet in an extension or alteration, of making things worse in terms of (M1) than before.

Enough said now? :)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
-
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
What will the outcome be of my assessment?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
76
Unsolved
--

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
rolyberkin,
Replies
76
Views
8,512

Advert

Back
Top