Called to a property which has just been sold to do an EICR
The sockets down stairs including the kitchen were on a 16a 2.5 radial the issue being the Zs for the first couple of sockets were about average readings but the last few and the sockets in the kitchen went from 0.90 ohms to 1.19 ohms. Personally I wouldn’t put a kitchen on a radial but that’s just my preference. But why the higher than normal results could it be a case of more than one spur from a socket That’s giving me high readings also 16a is just not cutting it. The property had an EICR done a few months ago but no concern over higher readings on socket radial for the down stairs sockets including the kitchen being on a 16a 2.5 cable your comments would be appreciated
 
I’m getting the feeling this might be a final ring broken into 2 radials - but maybe not correctly. Do you see 2 radials that could have been a ring. What you are describing doesn’t make sense. It’s factual and correct but nonsense at the same time. Your further investigation is crucial.
 
I’m getting the feeling this might be a final ring broken into 2 radials - but maybe not correctly. Do you see 2 radials that could have been a ring. What you are describing doesn’t make sense. It’s factual and correct but nonsense at the same time. Your further investigation is crucial.
I did notice a cable cut out int the kitchen and thought that myself I have asked the buyer to contact the previous owner to see if they could shine any light on any work that’s been done prior the sale

This is important. You might well have found the reason this is a such conundrum.
 
I’m not comfortable with the fact downstairs sockets and the kitchen are all on a 16a what do you think.

Nor would I be. Kettle and a toaster alone are likely to cause an overload and trip!
The readings for a radial are possibly ok but if a significant jump in Zs between sockets (unless long run of cable) then further investigation required as previously suggested.
As it is an EICR recommend upgrading to
 
Nor would I be. Kettle and a toaster alone are likely to cause an overload and trip!QUOTE]

A little pedantic of me but if it's a fairly typical kettle (3kw rating) and toaster (2kw rating) then they may not cause the MCB to trip at all as they will be pulling up to 21.73A max and (from memory so could be slightly off) MCBs must, as a minimum, trip at 1.45 times their rating in under an hour, in this instance 23.2A, so 21.73A may not be enough to make it trip ever, let alone within the 5 minutes the kettle is on.
 
I had to split a ring final in a non domestic premises last week, open cpcs which could not be rectified. Ended up with five outlets on one, seven on the other. Zs for one 0.64 the other 1.66. The low reading the first part of the circuit the high one went all the way over and back to the middle.
 
Thanks again for your comments. Just to update. I called the previous owner and asked if they could shed any light and after 10 minutes of uming and aring told me that he had an issue with the downstairs ring so the electrician he used cut one leg of the RFC and layed another cable to it and the rest is still on with the kitchen 16a
 

Reply to What’s going on with this radial in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
545
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
988
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
919

Similar threads

  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top