After 7 pages of all this (and yes I know the approved way of testing an RCD), I still like to test the RCD at the circuit/s I've worked on [such as additional sockets for example].
It's just good to know that you're actually simulating a fault where it might actually happen and seeing the disconnection times at the business end of the circuit as it were, gives me additional peace of mind.
So you get better peace of mind carrying out the test in such a way that could give a false pass?
Any earth leakage on the outgoing circuits will bias the RCD to trip at a lower test current than if it was tested in isolation.
With a 10mA existing earth leakage the tester could apply 30mA test current to trip the RCD yet the RCD is seeing 40mA before it trips.
No I do it at the RCD initially, for the sake of a few seconds I also do it at the end [unless it's a RFC] of the circuit/s in question - with all other final circuits switched off. So assuming the circuit in question has already undergone dead testing and produced good insulation resistance results how can there be earth leakage to confuse the tester ? If anything I'd expect to see slightly higher tripping times at the end of the circuit.
If the tripping times change due to the tester being at the end of the circuit then the RCD is faulty. If anything it may be quicker as RCDs tend to get a bit quicker after a few operations.
The tripping time will be exactly the same wherever you put the tester assuming that there is no earth leakage to interfere.
As far as the IR results go, what exactly are you calling 'good'? If there are a number of circuits then their combined insulation resistance may be quite a bit less than the individual circuits
Right! On your schedule of test results have a free line above each set of RCD protected ccts. Put on that line RCD 1/61008/x1/x5 results....then on your next line start the various cct details, and you can then also detail individual cct RCD results if you so wish...
That way everyone is happy (cept maybe DS!) !! :smile:
Good to see Trev back...
Reply to Whats this mean on a rcd test in the UK Electrical Forum area at ElectriciansForums.net
It can also mean lasts or continues for two years.
L
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...