Agree - I've forgotten all this now (if I ever really knew it) but I think the BS61439 sets this and DNO work to it and so our nice little boards handle faults faultlessly, in theoryWell most DB have a rated fault current of 16Ka
That is 16KA with the energy limiting of a 100A BS1361 / BS88 fuse between it and the supply.Annex ZB of BSEN 61439-3:2012 has a Deviation for the United Kingdom that states that distribution boards intended to be operated by ordinary persons with double pole isolation, normal protective devices and type tested for use with standard supply fuses should be able to withstand a specified test using a fault current of 16kA and not fall below certain levels of safety during and after the test e.g. not cause fire and not be significantly damaged or deformed.
Therefore all UK consumer units should be designed to withstand a 16kA fault current and so this is the maximum level you can specify on the EIC.
Yes so long as it has a standard supply fuse you should be OK, the test is with a 100A BS1361 / BS88 fuse.That is 16KA with the energy limiting of a 100A BS1361 / BS88 fuse between it and the supply.