Why does it try to give you the value of 16KA in the drop down box for prospective fault current. Has anybody else come across this or do they know the reason why? I always put my measured value in but still would like to know the reason they try to give you the above value.
 
Well most DB have a rated fault current of 16Ka
Agree - I've forgotten all this now (if I ever really knew it) but I think the BS61439 sets this and DNO work to it and so our nice little boards handle faults faultlessly, in theory :)
Can anyone clarify please?
 
You'll find in the notes section it explicitly states that this should not be a measured value. That is why it defaults to 25kA/16kA.
 
Annex ZB of BSEN 61439-3:2012 has a Deviation for the United Kingdom that states that distribution boards intended to be operated by ordinary persons with double pole isolation, normal protective devices and type tested for use with standard supply fuses should be able to withstand a specified test using a fault current of 16kA and not fall below certain levels of safety during and after the test e.g. not cause fire and not be significantly damaged or deformed.

Therefore all UK consumer units should be designed to withstand a 16kA fault current and so this is the maximum level you can specify on the EIC.
 
Annex ZB of BSEN 61439-3:2012 has a Deviation for the United Kingdom that states that distribution boards intended to be operated by ordinary persons with double pole isolation, normal protective devices and type tested for use with standard supply fuses should be able to withstand a specified test using a fault current of 16kA and not fall below certain levels of safety during and after the test e.g. not cause fire and not be significantly damaged or deformed.

Therefore all UK consumer units should be designed to withstand a 16kA fault current and so this is the maximum level you can specify on the EIC.
That is 16KA with the energy limiting of a 100A BS1361 / BS88 fuse between it and the supply.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London

Thread Information

Title
When Filling Out A N.I.C Installation Certificate Online *DEFAULT PFC VALUE*
Prefix
N/A
Forum
Electrical Tools and Products
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
EM4Z1NG,
Last reply from
Richard Burns,
Replies
12
Views
2,084

Advert

Back
Top