If it enters as TN-S you have to consider it as such. But I agree in most cases now it is likely to be PME/TN-C-S outside.
 
The thing is the DNO call it pme. We call it tncs. As far as we are concerned as Westwood said, if it it tns as it enters a property that is what we should treat it as.

There is a difference between tncs (tera neutral combined seperate) and pme (protective multiple earthing). You can have tns and a pme system and that is the difference
 
If it’s tncs outside but separate earth entering the property then I’d imagine the dangers or an open circuit neutral in the road will still cause Potential for danger in the installation regarding exposed conductive parts rising to or near mains potential as any tncs installation would.
 
I think it would be inadvisable to 'assume' the DNO supply to be PME if it appears TNS at the service head. If for some reason the supply is thoroughbred TNS then creating a N-E link anywhere would split the neutral current at best and could result in enormous current through that link in the case of an upstream DNO neutral fault in the future.
 

Reply to When is TNS really PME and vice versa? in the Electric Vehicles Advice Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
515
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
754
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K
Glad to hear you approve @Moley
    • Like
    • Winner
Replies
3
Views
384

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top