Installing an over the range microwave, ran the (yellow) wire to the box, but where can I attach the ground and neutral wires? The one bus on the right is full, the second bus on the right is empty, but can I use it? Nothing else is attached to it.
Something is going wrong with our communication.
How can either A or B be phase connections when they have both neutral and ground conductors connected to them?
It may appear to all be together but turn all power off a read on the OHMS scale. Phase A and B will not read to ground. I think that you need a licensed electrician to help you
I am finding my patience tried, so I hope this doesn't seem unacceptably aggresive:
None of the bars which I have labelled A, B and C are phase terminals.
None of the conductors connected to the bars which I have labelled A, B and C are phase conductors - they are all neutrals or grounds.
So what are A, B, and C, and which have continuity?
I think perhaps MW is referring to the two incoming phases as A and B.
I read your profile and are you in the UK ? If you are referring to the US way of panels the left screw is 1 live terminal, the middle screw is your neutral and the screw on the right is your other live terminal. The middle screw is attached to the ground bar and neutral bar. The right screw and left screw are attached to the phase conducters . I don’t know what else to say. Hire an electrician
Sigh.
Just as per the label in my post #13, what is the bar I have labelled A, which has a mix of bare and white-sleeved conductors to it? I find it really hard to believe that it is, as you replied in #14, a phase terminal.
Just as per the label in my post #13, what is the bar I have labelled B?
Just as per the label in my post #13, what is the bar I have labelled C, which has a mix of bare and white-sleeved conductors to it? I find it really hard to believe that it is, as you replied in #14, a phase terminal.
And what continuity, if any, exists between A & B, A & C or B & C?
Sigh.
Listen my friend the bars you have labeled A B C is the neutral/ ground bar which is legal by code, any panel sub fed from this panel you have to keep the neutrals separate from the grounds. A B C are all connected to the lug on top in the middle. As far as continuity A B and C WILL read together
Soi, I don't think MW saw the a,b,c labels that you added to the picture. He was referring to A and B as the 2 incoming phases. Hence the confusion.
I think we all knew the neutral and earth bars weren't connected to the phases.
None of this is helping the OP of course.
So he didn't see the photo in my post which he quoted when replying.
OK.
Indeed, but as I never in a million years considered the possibility that when he replied to #13 which had a large photo with quite vividly coloured labels on it and text which explicitly referred to them he hadn't actually looked at the photo, I wondered WT.. was going on.
No, but it does seem to have been unfortunately much prolonged - all I was after was clarification of what MW said at the end of this sequence:
Surely it's all the same piece of metal?
No it’s not, the neutral bar has an insulator on the bottom and is not an integral part of the panel, the ground bar doesn’t have an insulator
Because that separation of N & G (perfectly believable) would mean that the N & G conductors should not be connected together as they are.
OK.
Sol I hope your not an electrician because that would be an accident waiting to happen. Just because I missed your A B C stickers doesn’t mean I gave you the wrong advice. What you have is perfectly legal in your first panel after the power company’s meter and for the 5th time you have to separate the grounds from the neutral. If you know it all we should be asking you for advice, and since you don’t have a clue about electrical you need to find something else to do.
Megawatt, Soi isn't the original poster. The OP hasn't been on here since April 18th.
For at least the third time, it's not my panel.
You've missed reading that.
You've missed seeing the labels on my photo.
You say you've not given wrong advice when you've said both that the N&G bars are not one and the same and that they are.
You're the last one who should be lecturing others on their competence.
I'm done here now.
I'm done here now.
Maybe there have been some misunderstandings on this thread, but Megawatt is a respected member on here.
Reply to the thread, titled "Where to attach neutral/ground in breaker panel" which is posted in USA Electrical Forum on Electricians Forums.
USA Electrical Advice
Welcome to the USA Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This is the main UK Electrical Forum at ElectriciansForums.net. Electrician Laws and Regulations related to Electrics and Electricals within the United Kingdom. Electrician talk, questions and answers can be found in our UK electrical forum.