Is there such thing? The regulations assume a partition in the zoning. In this scenario the shower is a box room of about 1m by 2.5m with the shower in the far end and the loo and basin to the door. There was once a heater with the fused spur external in the hallway. Since then the shower now has been effectively turned into a wet room but the customer is elderly and feels the cold and there is no other heating in the room bar a small electric towel rail. What could I possibly fit?
 
Use a bathroom down flow fan heater (IP 44 or better) outside the wet room zone one (so other end of room from shower), no switches in zones and RCD protection to circuit.
 
What about those tubular heaters? Never used them before so dont know if they are any good or not, but seen some on TLC that are IP55. Follow advice above too of course.
 
Tubular heaters are used where they are providing heat to an area in the same manner as a central heating radiator.
A bathroom fan heater however, is only used for short periods of time, usually only for the duration of bathroom occupation. Hence the fan heater will have a much higher KW rating than the tubular space heating setup!!
 
What about those tubular heaters? Never used them before so dont know if they are any good or not, but seen some on TLC that are IP55. Follow advice above too of course.

If you use them for the potting shed or animal / chicken cot or garage workshop etc they are excellent
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Hampshire

Thread Information

Title
Which electric fan heater can be a in shower/wet room?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
vee,
Last reply from
vee,
Replies
8
Views
10,735

Advert

Back
Top