hi all,
looked at this job today and not 100% sure of the system.
Ze is 0.15 suggesting tncs but look at the 16mm earth.
the cables disappear througn the wall, under a garden path that has bee dug up and replaced to enable the install and then are nowhere to be seen.
apparently it was done quite recently but no certificate was left with home owner.
 

Attachments

  • [ElectriciansForums.net] which system
    P1010625.jpg
    28.7 KB · Views: 35
  • [ElectriciansForums.net] which system
    P1010626.jpg
    37.2 KB · Views: 38
There wouldnt be a cert if its the supply as the DNO's dont issue them.

I would say its a TT.

No cpc coming from the cutout.
 
Agree with Jason,definitely a TT.Did the customer have the board moved?Have you found a spike outside?All the cabling,meter and main fuse look brand new
 
Last edited by a moderator:
Is it an annex or something.As Jason said,there is no earth at the incomer.Could be a TNCS if it is fed from somewhere else:confused:
hi mac,
judging by the Ze i would say its tncs, but like you say theres no earth in the cutout :confused:
apparently the gas board came round to repair a leak and damaged the incomer.
it was repaired and i would say there could be some sort of joint below the garden path.
surely they wouldnt have joined it below ground and run the cables up separately would they :confused:
 
Nothing would surprise me.

I think you need to trace those cables and find out whats what.

There is no reason why a TT would not be that low, although it is quite rare.

I think a call to the DNO is needed first to find out exactly what they did.

If they installed a PME system then it should have been labeled as such.
 
hi mac,
judging by the Ze i would say its tncs, but like you say theres no earth in the cutout :confused:
apparently the gas board came round to repair a leak and damaged the incomer.
it was repaired and i would say there could be some sort of joint below the garden path.
surely they wouldnt have joined it below ground and run the cables up separately would they :confused:
Don't know why they don't put inspection pits in like BT if they joint cables.Are there no signs of anyone digging up the road.What has the customer said:confused:If the DNO came round to repair the cable,should they not have it on there system.Still:confused:
 
Last edited by a moderator:
Nothing would surprise me.

I think you need to trace those cables and find out whats what.

There is no reason why a TT would not be that low, although it is quite rare.

I think a call to the DNO is needed first to find out exactly what they did.

If they installed a PME system then it should have been labeled as such.
the only way to trace the cables is to dig their garden path back up, something im not prepared to do:p
have to call dno tomorrow and find out what it is.
definitely cant be tt as the are no poles in the area and no overheads.
cant say ive ever had a reading as low as 0.15 on the few tt installs ive worked on in the past :confused:

Nothing would surprise me.

I think you need to trace those cables and find out whats what.

There is no reason why a TT would not be that low, although it is quite rare.

I think a call to the DNO is needed first to find out exactly what they did.

If they installed a PME system then it should have been labeled as such.

Don't know why they don't put inspection pits in like BT if they joint cables.Are there no signs of anyone digging up the road.What has the customer said:confused:If the DNO came round to repair the cable,should they not have it on there system.Still:confused:
the only sign of digging is on the path. the couple who own the house are elderly and havent got a clue what was done
 
Last edited:
0.15 on a TT, rare......sorry to disagree mate but no way. You'd have to bury a grid the size of Scotland to achieve a Ze like that on TT.
 
No i know and it is rare.

However, it could be something as ridiculous as them not having the correct cable to carry out the repairs and only had straight con on the van.

This could be the reason why there is a separate earth as this may be attached to the lead sheath underground.

Yeehah!!!!!!!!!!!
 
However, it could be something as ridiculous as them not having the correct cable to carry out the repairs and only had straight con on the van.

This could be the reason why there is a separate earth as this may be attached to the lead sheath underground.

I would agree with that theory.;)
 

Reply to which system in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
183
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
560
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
516

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top