We all know that if something is extraneous then it needs to be bonded. However, if we have some water pipes in a bathroom for example that test at 0.2Ω to earth (MET) would you be happy with that? Let's assume it has RCD protection. I realise some say that if the extraneous tests at <1667Ω then the RCD will trip before the potential rises to 50V, however I don't feel very comfortable with this as the RCD is for 'additional' protection.
GN3 states that if the resistance to earth of the extraneous is <0.05Ω then we can assume the extraneous is bonded. So, my question is 'would you feel it necessary to take a separate bond to the pipes in question in the above example as they are > 0.05Ω? If you are happy with this then what resistance would you feel is a maximum before you feel the extraneous needs bonding?
With Zs figures there are very clear limits. The only limit I can see in these sort of examples is 0.05Ω.
GN3 states that if the resistance to earth of the extraneous is <0.05Ω then we can assume the extraneous is bonded. So, my question is 'would you feel it necessary to take a separate bond to the pipes in question in the above example as they are > 0.05Ω? If you are happy with this then what resistance would you feel is a maximum before you feel the extraneous needs bonding?
With Zs figures there are very clear limits. The only limit I can see in these sort of examples is 0.05Ω.