:confused: If tails from meter/ isolator to CU belong to the customer, is said customer required to notify supplier when having the length of the tails extended?

:eek: Would someone please explain the why, what and where of a switchfuse used when extending tails. Thank you.
 
Depends on how long the tails are to be extended by.
Call DNO & ask what max length of tails they will allow without switch fusing.
You'll need to call them anyway to arrange for a meter monkey to visit & pull service fuse, (you cant work live to extend the tails) while you work then refit the fuse.

Why:
Because in effect the tails become a submain & as such will require a cpc + ocpd suitably rated for the load length of submain & csa of cable.

WHAT:
Wylex 100 Amp SP&N Switchfuses
or something like this will do so long as the mcb is rated high enough
100 Amp Main Switch for Sentry Consumer Unit
50 Amp MK MCB
4 Way Insulated Enclosure

WHERE:
Ask nicely and DNO will let you put it in the meter cupboard.
Failing that at a length of meter tail that the DNO say is ok before a SF is required (normally 3mtrs)
 
Thank you for responding EasyFox, the lightbulb hasn't quite gone on in my head yet though. Would you mind following up with my questions below?

Why:
Because in effect the tails become a submain & as such will require a cpc + ocpd suitably rated for the load length of submain & csa of cable.

Why do the tails become a submain? If the tails were split, after the meter and isolator, for two CUs - are these now submains? [I think I'm not actually clued up on what a submain is - I had thought it was a distribution board coming from an mcb way in an upstream CU :eek:]

If the switchfuse protects the length of tails between meter and CU, why is not having one for 3m tails ok, but not for say 15m tails?

Thank you. :)
 
The DNO are not responsible for the design of the installation so they require an over-current protective device to be fitted if tails exceed 3M to protect them.

So, basically, if you dont, they are well within their rights to cut off your supply as the above is usually a requirement for the supply of electricity to the premises.
 
Last edited by a moderator:
ok, thanks for that Jason. I'll accept that that's the way it is, though if the tails are the customer's, then why are the DNO involved? If the DNO's supply cable went 15m further, do they make any adjustments to the fuse fitted?

As you can see, I've not quite got it :confused: Sorry.
 
ok, thanks for that Jason. I'll accept that that's the way it is, though if the tails are the customer's, then why are the DNO involved? If the DNO's supply cable went 15m further, do they make any adjustments to the fuse fitted?

As you can see, I've not quite got it :confused: Sorry.
I think you may be trying to look into it too deeply.;)
 
I think you may be trying to look into it too deeply.;)

You're right, I'll let go of it :cool: ..time to find another bone to worry.

I keep six honest serving-men
(They taught me all I knew);
Their names are What and Why and When
And How and Where and Who.

...la la lalala la...

But different folk have different views; :D
 
but are they?

the tails are connected to the meter, and that is not the DNO's, that is your electricity suppliers, your DNO's property ends at the incoming fuse:cool:

Thats correct, however, the DNO own the supplying cable, fuse etc (the important bit). the meter is only to monitor usage, not to provide any fault protection.

Therefore, they have the final say on how you connect your installation to THEIR supply.

Some DNO's will not connect a new supply without seeing an install certificate from an NICEIC or ECA registered member.

You are thinking far too much about this!!!
 

Reply to whose tails and how would you like it sir? in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
644

Similar threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K
Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
234

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top