Discuss Why are main protective bonding conductors sized as they are in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I have a feeling you might be rightThen Only the people who write chapter 54 could possibly give the answer?
By this, do you mean when disconnection times can't be met in the event of a fault, the potential difference between exposed conductive and/or extraneous parts mustn't rise above 50V? Or am I getting mixed up?Aren't CPC's and bonding conductors sized around allowing a maximum of 50 volts elevation under worst case fault conditions? 5o volts being the arbitrary figure that would limit earth leakage to 30mA through anyone in contact with something earthed or bonded.
Other than the PME fault current issue, the factor I would say is important is the consequence of failure.There has to be another reason for the larger minimum CSA required for bonding conductors other than durability.