Aren't CPC's and bonding conductors sized around allowing a maximum of 50 volts elevation under worst case fault conditions? 5o volts being the arbitrary figure that would limit earth leakage to 30mA through anyone in contact with something earthed or bonded.
 
Aren't CPC's and bonding conductors sized around allowing a maximum of 50 volts elevation under worst case fault conditions? 5o volts being the arbitrary figure that would limit earth leakage to 30mA through anyone in contact with something earthed or bonded.
By this, do you mean when disconnection times can't be met in the event of a fault, the potential difference between exposed conductive and/or extraneous parts mustn't rise above 50V? Or am I getting mixed up?
 
There has to be another reason for the larger minimum CSA required for bonding conductors other than durability.
Other than the PME fault current issue, the factor I would say is important is the consequence of failure.

If your main earth bond fails then everything in the system is at risk, not some sub-section, and the could result in significant accumulated leakage currents even without a fault leading to phase current flowing. If your main RCD on a TT system is 100mA or 300mA, both of which are perfectly good if your circuits have instant 30mA RCD protection, you could see a risky leakage between the system earth and true earth without tripping.

I really have no idea about the drafting of the regs, but that would be my worry.

Edit to add: Also what if you have an SPD that might divert a few kA on a surge? Adiabatic might need consideration for that.
[automerge]1586209211[/automerge]
I think a 25kA lightning pulse (the "direct" 10μs/350μs waveform) would require 4mm, so not a likely reason and I doubt most UK sites would ever see that.
 
Last edited:

Reply to Why are main protective bonding conductors sized as they are in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
488
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
962
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
901

Similar threads

I don't think I'd use it mate even the one line heading then one long paragraph screams ai. And untrustworthy. I don't think much has been edited...
    • Optimistic
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top