Can someone explain electrically why we can spur unfused from a ring final on a 32a breaker when the cable is 2.5mm rated at max 27a?
 
As bove , the maximum current draw ( in theory ) will only reach 26 amps. but as we all know a 13a fuse will run way over 13amps so in reality its a folly rule but a rule none the less
 
As bove , the maximum current draw ( in theory ) will only reach 26 amps. but as we all know a 13a fuse will run way over 13amps so in reality its a folly rule but a rule none the less
I'm not so sure it is a folly rule Dusty. I thought the same as you a few years back,.

An MCB (or even more so a fuse), will pretty much run for ever at it's rated current, or even a little above it. Even at say 20% more current running through it, it will still run for quite some time (20% is a guess, just to show the point although I haven't looked at the time/curve graph). I believe BS7671 takes this in to account, so in fact the insulation of the cable can take more than the CCC quoted in BS7671.

In fact, I'll give a proper example.

A 5A BS3036 fuse will take 0.75 secs to blow with 20A of current running through it. If it is wired in 1mm, then the 20A is too much, but I believe the cable would be designed to take this amount of current for (at least) the time given from the time/current graphs.

I would have thought this is the same for a 13A fuse (with slightly different actual figures).

This is a bit of guess work though, and I'm really not sure if it's right. Just seems logical that cable should be designed to take whatever current could be drawn until the fuse blows (as long as the electrician has designed the circuit correctly).
 
I'm not so sure it is a folly rule Dusty. I thought the same as you a few years back,.

An MCB (or even more so a fuse), will pretty much run for ever at it's rated current, or even a little above it. Even at say 20% more current running through it, it will still run for quite some time (20% is a guess, just to show the point although I haven't looked at the time/curve graph). I believe BS7671 takes this in to account, so in fact the insulation of the cable can take more than the CCC quoted in BS7671.

In fact, I'll give a proper example.

A 5A BS3036 fuse will take 0.75 secs to blow with 20A of current running through it. If it is wired in 1mm, then the 20A is too much, but I believe the cable would be designed to take this amount of current for (at least) the time given from the time/current graphs.

I would have thought this is the same for a 13A fuse (with slightly different actual figures).

This is a bit of guess work though, and I'm really not sure if it's right. Just seems logical that cable should be designed to take whatever current could be drawn until the fuse blows (as long as the electrician has designed the circuit correctly).
I agree with what you are saying and several youtube spraks have shown a short bit of 2.5 cable run 50-60 amps before its tarts to get hot,
my point is if you have a ring it should be kept a completed ring , allowing spurs , spider legs and lolly pops you might as well just fit radials in the first place and do away with ring mains
 
if you are going to spur off a ring circuit it's 2.5mm for a single socket and 4 for a twin.
UMM, No, that means you will have 2x2.5mm and 1 x 4mm in a socket, lets face it spud that just isn't going to happen, I have seen it but it isn't the way.
 

Reply to Why can we spur unfused from rings? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

  • Question
Take it up with the IEE.....but they won't explain it any better than you've seen already.
Replies
13
Views
2K
  • Question
Cheers guys, enjoyed reading all the responses. I'm an apprentice and it was a conversation that came up at work between two electricians...
2 3
Replies
43
Views
3K

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top