Why did the Ra go from 180Ω to 14Ω? | on ElectriciansForums

Discuss Why did the Ra go from 180Ω to 14Ω? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Supporter
Joined
Dec 18, 2011
Messages
5,348
Reaction score
6,600
Location
Gloucestershire
About a year ago I went to a property to do some work. It is a TT and the Ra was something like 300Ω or 400Ω, I cant remember exactly. I put in 2 new rods 5/8" and it came down to around 180Ω, still poor but <200Ω.

I went back today for some more work and the customer said an electrician had been out next door and got Western Power (WP) out with regards 'something to do with the earthing'.

Before I started my work I checked the Ra as I wanted to make sure it was stable at <200Ω. It measured as 14Ω.

My customer took me to the electricity pole (I guess this is the transformer) on her property (large field) and showed me where she thinks the work was carried out. On either side of the pole is a cable which runs into the ground, one of these is where she thinks the work was carried out. What would WP have done to improve the Ra? I thought the Ra was related just to the customers earthing system, i.e rod etc.
 
Id agree with Sparkychick.
Answering your question, RA is the sum of the resistances of the earth electrode (to Earth) and its using the mass of earth as its conductor, so a nice new earth at a transformer would reduce your reading.

Sounds like your pretty close to the transformer so if you were getting a reading of 400ohms other people down the road probably had readings up in the 1000 I expect someone complained so DNO had to sort it out.
 
Would not dream of doing so,friend.
Just imagine the tasks one would perform,either intentionally,or deliberately,to improve the Ra on a particular installation.
Now consider,if any work or task,agents from a DNO would or could carry out,and how this could affect things.
 
Would not dream of doing so,friend.
Just imagine the tasks one would perform,either intentionally,or deliberately,to improve the Ra on a particular installation.
Now consider,if any work or task,agents from a DNO would or could carry out,and how this could affect things.

I honestly swear I cannot think of anything.
 

Reply to Why did the Ra go from 180Ω to 14Ω? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
1K
Heh I know the brochures for courses with stock images of women using tools in random scenarios but when you're there it never happens, it's all...
    • Like
Replies
2
Views
420

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top