I'm doing testing on landlords' supplies in blocks of flats for a london borough, the other week I was asked to PIR a flat which was having prepayed meter fitted (the switchroom is kept secure so tennant wouldn't be able to access the meter).
The flat had been rewired a matter of weeks previously and here's a rough list of my comments on the PIR...
no rcd label
no inspection label
no harmonised wiring label (roomstat wiring was existing 3 core+earth)
missing blanks in consumer unit
absent main protective bond to water service (they had tried to piggy back from the gas bond but had used a 50mm through crimp which fell apart!!!!)
4x double sockets unspurred from ring circuit
loose connections in almost all accessories
NO MAIN EARTH CONNECTED!!!!!!!!!
I forget the rest but I truly have never seen such an awful installation, it looked like whoever did it had absolutely no idea. There was skirting trunking throughout and instead of stripping out the existing wiring and using that they ran YT2 all over the place, massive gaps at joints and bends, diagonally across ceilings to light fittings and all sorts.
This is a COUNCIL owned flat but had no completion certificate. The council employed the subbies who installed it so how does that work? A domestic customer has to pay extra for an registered sparks who will have to go through the rigmarole of notification etc but as the council own the property all that goes out the window???