I was wondering why the tails need to have a switch fuse if longer than 3m?
I have hunted through the threads and most say that the DNO only allows their cut out fuse to protect the tails up to 3m but why is this? In theory we could just put the switch fuse 1m into the 3m run.. how is that helping having another fuse 1m from the cut out. Also if the cut out is 60A you will just be putting another 60A KMF??
Regulation 433.2.2 states:
"The device protecting a conductor against overload may be installed along the run of that conductor if the part of the run between the point where a change occurs (in cross-sectional area, method of installation, type of cable or conductor, or in environmental conditions) and the position of the protective device has neither branch circuits nor outlets for connection of current-using equipment and fulfils at least one of the following conditions:
i It is protected against fault current in accordance with the requirements stated in in Section 434.
ii Its length does not exceed 3m, it is installed in such a manner as to reduce the risk of fault to a minimum....."
So is that saying that if we meet the requirements in the above paragraph AND point (i) then we don't need a additional switch fuse?
Cheers all, looking forward to the responses on this one..
I have hunted through the threads and most say that the DNO only allows their cut out fuse to protect the tails up to 3m but why is this? In theory we could just put the switch fuse 1m into the 3m run.. how is that helping having another fuse 1m from the cut out. Also if the cut out is 60A you will just be putting another 60A KMF??
Regulation 433.2.2 states:
"The device protecting a conductor against overload may be installed along the run of that conductor if the part of the run between the point where a change occurs (in cross-sectional area, method of installation, type of cable or conductor, or in environmental conditions) and the position of the protective device has neither branch circuits nor outlets for connection of current-using equipment and fulfils at least one of the following conditions:
i It is protected against fault current in accordance with the requirements stated in in Section 434.
ii Its length does not exceed 3m, it is installed in such a manner as to reduce the risk of fault to a minimum....."
So is that saying that if we meet the requirements in the above paragraph AND point (i) then we don't need a additional switch fuse?
Cheers all, looking forward to the responses on this one..