I've had to have my immersion switch replaced 2-3 times over the last few years, the guy I had do it isn't a professional so I'm thinking he's wiring it wrong? I wired this one myself based on what way he had it wired the last time. It seems to be the blue wire that gets warm and melts everything else.

IMG_0478.jpeg
 
What's the deal with the short link in the Lout terminal?
 
What's the deal with the short link in the Lout terminal?
Link is to a 2W 20A switch, that selects between two immersion heater elements.
The green/yellow used for the link looks a little undersized, so might warm things a little, and it looks like the back box might be a bit short of room, but other than that there's nothing wrong that stands out.
 
Link is to a 2W 20A switch, that selects between two immersion heater elements.
The green/yellow used for the link looks a little undersized, so might warm things a little, and it looks like the back box might be a bit short of room, but other than that there's nothing wrong that stands out.

Ah just saw the g/y earth colours and didn't look much further.

Usual suspects would be cheap/old accessory and/or poorly made connections.
 
When you rewired the last switch, you say the blue wire had overheated - was the copper a darkened/ oxidised colour?
And were other wires affected by heat?
The discolouration can give poorer surface conductivity, and the heat can make the copper softer, both of which can lead to a poorer quality termination if the overheated switch is replaced without dealing with the damaged cable ends.
It's best, if you can, to cut the wire(s) back so that you get to shiny unoxidised copper to make new joints with.
If you did this when you last changed the switch, then I would blame the switch for the problem!
 
When you rewired the last switch, you say the blue wire had overheated - was the copper a darkened/ oxidised colour?
And were other wires affected by heat?
The discolouration can give poorer surface conductivity, and the heat can make the copper softer, both of which can lead to a poorer quality termination if the overheated switch is replaced without dealing with the damaged cable ends.
It's best, if you can, to cut the wire(s) back so that you get to shiny unoxidised copper to make new joints with.
If you did this when you last changed the switch, then I would blame the switch for the problem!
I didn’t cut them back as much as I probably should have. I will try that with the next switch. Thanks
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Ireland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
Ireland
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Why does my immersion switch keep melting?
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
6

Thread Tags

Advert

Thread statistics

Created
Mk-blg,
Last reply from
Mk-blg,
Replies
6
Views
995

Advert

Back
Top