I take it you're allowed to use radials for sockets?

So why does anyone bother with rings, seems like extra hassle to me.
 
Oh this will open a can of worms when it comes to the arguments for and against ring final circuits!

Yes, you can use radial circuits and in the UK case with any number of sockets, subject the maximum typically of a 32A MCB feeding cable of adequate size.

Similar for a ring, but there you can use less cable and/or longer route, again no limit to sockets as such, but total is limited to typically 32A (some older systems would have a 20A fuse or MCB).

The key difference with the UK are really the fused plugs. That came from the idea of having a standard plug/socket for all normal loads but a choice of fuse, instead of the old arrangement of radials with different feed fuses each for a single socket, and different plug sizes so you could not plug a 2A appliance in to a 15A feed.
[automerge]1587590880[/automerge]
Advantages of the ring:
  • Less copper for a given load / area
  • No single point of failure for protective earth
Advantages of radial:
  • Simpler idea
  • Faults show up immediately
While for some it almost gets to a religious argument, in general if you only need a few sockets then a radial is best choice, if you are covering all rooms in one floor then a ring is probably better able to do it.
[automerge]1587591564[/automerge]
For the history try a search for "THE ORIGIN OF THE BS 1363 PLUG AND SOCKET OUTLET SYSTEM" as there is an IET publication from 2006 with details.

For a quick idea of what you can do with ring or radial in practice then the IET's On-Site Guide book has "Table 7.1(i)" giving the typical cable length limits for ring final circuits on page 65, and for radial final circuits on pages 68-73
[automerge]1587592017[/automerge]
In case you don't have that book, some numbers are:
  • Ring final 2.5mm cable, 32A B-curve MCB, length 106m on TN-C-S
  • Ring final 4mm cable, 32A B-curve MCB, length 171m
  • Radial final 2.5mm cable, 25A B-curve MCB, length 33m
  • Radial final 4mm cable, 32A B-curve MCB, length 43m
 
Last edited by a moderator:
How does a ring use less copper?

A radial is basically a ring without the return cables. Confused!
because to crate a 32A radial, you need to use 4mm or 6mm cable. and a radialcould well end up with the last socket alomost back to the board, so the extra leg of a ring might be only a few yards.
 
How does a ring use less copper?

A radial is basically a ring without the return cables. Confused!
As already mentioned by @telectrix because the ring can use smaller cable for the same overall rating. Almost all final ring circuits in the UK use 2.5mm cross sectional area cables for a 32A rating, to do the same total current as a radial you need to use 4mm (saving in copper of typically over 30%) or even 6mm if the length is great.

The other thing you might not have realised is the UK difference due to fused plugs, here we can put on as many sockets as we want to either type of final circuit. Where as in most of the rest of the world the plugs are unfused so the supplying breaker has to be small enough to protect the final cable against fire, so often that makes for more expensive final cables as well as more radials per house as there is a limit on the number of sockets per radial.

Now the fact we can put on as many as we want per circuit does not mean we should! The higher total capacity (typically 32A) means better load diversity is possible, but even then in the UK you would often plan for more than one final circuit for several reasons:
  • Fault resilience
  • Expected load distribution
  • Expected total load
As a "rule of thumb" you would be using in the UK one ring final per floor in a multi-story property, and even with a single floor flat you might plan for a separate ring for the kitchen where the majority of power-hungry appliances tend to live (washing machine, tumble dryer, dishwasher, etc).

Finally in the UK radial circuits are still very much alive and well for large fixed loads (such as cookers or larger air conditioning units), and for cases when you really don't want an unrelated fault to deny power to somthing critical (e.g. fridge-freezer might have its own breaker, or computer UPS supply in a home/office arrangement, etc).
 
Last edited:
I suppose we could go with the French method of radials. But hang on, it's a nightmare testing such circuits where there are branches and additions of various kinds and you end up with a radial circuit that is a tangle and very hard to determine what is connected to what. Hence the British like ring circuits because even where mistakes are made you have a beautifully mathematical way of deducing what has happened. The logic intrinsic in the ring circuit and testing methods are second to none throughout the world.
 
@Vortigern also raises the issue of circuit testing. A common complaint by folk looking at testing for the first time is the test procedure for ring final circuits looks unusual, and they think it is more complicated and time-consuming.

It is, but that misses the point! The ring test procedure also provides much more comprehensive fault coverage than it is easy to do with a radial circuit.

The loop impedances (end to end for L-L, N-N, and E-E) give you a good indication of bad joints if you see they are not matching (L & N should be around 0.05 ohm or less difference) or in ratio (typically E/L is 1.67 due to the 1.5mm earth versus 2.5mm phase size used with our T&E cable). This is also easy to do for an inspection as you can do it all at the consumer unit (fusebox).

The "figure of eight" test (L1 joined to E2 and L2 to E1) not only allows socket polarity to be verified (i.e. L and N are correct way round) but is also quite a good test of socket quality as each socket should have practically identical resistance (L to E in this case), and any showing an increase of 0.05 ohm or so might be poorly connected or tarnished contacts, etc. Now 0.05 ohm may not sound like much, but at 10A that is 5W dissipated!
 
No we are populating DB's with RCBO's do you think that radials will become the norm, what do the team think? :cool: can't find a smily that sit's on the fence. :innocent:
 
Do you think that manufactures will standardise with the rest of the world and produce dual module RCBO's and get rid of the flying lead?
 
Do you think that manufactures will standardise with the rest of the world and produce dual module RCBO's and get rid of the flying lead?
Schneider produce rcbos with no neutral fly lead on their acti 9 isobar P DB’s, think the rcbo’s are only single pole tho.
DP rcbo’s are not necessarily required tho, be it a TN or TT arrangement, there’s no requirement to disconnect or switch the neutral during overcurrent conditions apart from those requirements detailed in part 7 of bs7671.
 
Last edited:
I don't see any need for them to be double-width, but for sure we should be moving to double-pole switching to make testing easier, and to have a neutral busbar arrangement in place so less effort and uncertainty in wiring the flying leads up.

There is the same problem for 3-phase where RCBO are rare and often need a 2nd slot for an add-one trip unit. Again, why not a neutral bar to all positions on the 3-phase system so you can have 3*single phase RCBO or 1 * three-phase, etc, per slot?

I have not played with the Schneider system to see how well it works, or if it addresses all of these things.
 
no neutral or no earth?
No fly leads on either

Isobar P is the first LV distribution board to have a plug-on RCBO (residual-current circuit breaker with overcurrent protection) capability. RCBO neutral and functional earth connections are usually wired into the neutral and earth terminals inside the distribution board, costing significant time by introducing additional wiring. With the new Acti9 Isobar P, installers can simply plug their RCBO directly into the board. This eliminates the need to cut, straighten or dress any excess wiring therefore reducing installation time by half.
 
No fly leads on either

Isobar P is the first LV distribution board to have a plug-on RCBO (residual-current circuit breaker with overcurrent protection) capability. RCBO neutral and functional earth connections are usually wired into the neutral and earth terminals inside the distribution board, costing significant time by introducing additional wiring. With the new Acti9 Isobar P, installers can simply plug their RCBO directly into the board. This eliminates the need to cut, straighten or dress any excess wiring therefore reducing installation time by half.
not seen these as yet.
 
not seen these as yet.
See link above
[automerge]1587651329[/automerge]
Contactum make dual pole RCBO's to international standard which in France, Switzerland and Germany it is a requirement to disconnect the neutral on activation: 40 Amp 30mA RCBO - 2 Module - Contactum - https://www.tlc-direct.co.uk/Products/CPBR402.html
2 modules is Far too big for some of the domestic CU’s and won’t fit in 3phase DB’s
Wylex and Crabtree do a single module type which is DP
 
Last edited:
2 modules is Far too big for some of the domestic CU’s
Wylex and Crabtree do a single module type which is DP
I went with Wylex for that reason, but in my case it is more about ease of testing.

Another difference is in the UK a TT supply with a RCD incomer is relatively rare so you don't usually have to worry about a N-E fault tripping the RCBO and that, if single pole, will not isolate the N fault so the main incomer RCD might also trip.
[automerge]1587652030[/automerge]
Unfortunately the Wylex DP RCBOs are not approved for use in their 3-phase boards. Doh!
 
I went with Wylex for that reason, but in my case it is more about ease of testing.

Another difference is in the UK a TT supply with a RCD incomer is relatively rare so you don't usually have to worry about a N-E fault tripping the RCBO and that, if single pole, will not isolate the N fault so the main incomer RCD might also trip.
DP rcbos is definitely a consideration and necessary for that reason but you can have a domestic CU with just a mains switch isolator giving you your DP isolation and just single pole rcbo’s for the final circuits. Same principle for 3 phase, as long as the tails are subject to non movement and enter a ferrous material in a suitable gland etc, and are the insulated and sheathed type
[automerge]1587652277[/automerge]
[Unfortunately the Wylex DP RCBOs are not approved for use in their 3-phase boards. Doh!
[/QUOTE]
Why not?
If it’s because of them being only 6Ka then they don’t necessarily need to be greater than 6Ka, all would depend on the PFC and if there’s sufficient back up protection/ coordination if the breaker can’t break the fault current.
 

Reply to Why does the UK use rings for sockets? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Luckily when I rejigged the socket to fit the fcu next to it, it meant the original ring wiring reached, i put the socket on the ring and took a...
    • Like
Replies
8
Views
1K
  • Question
Why aren't you asking them?
Replies
5
Views
777
  • Question
Yes that will do the job - presuming there is a battery in it and it's working Ok! Turn the rotary knob one click to the V setting as you say...
Replies
22
Views
2K
  • Question
Thank you for the speedy response! Have seen them on top of plaster in steel conduit before but guess it's not a common desire to have wires...
Replies
2
Views
610

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks