no neutral or no earth?Schneider produce rcbos with no neutral fly lead on their acti 9 isobar P DB’s, think the rcbo’s are only single pole tho.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Why does the UK use rings for sockets? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
no neutral or no earth?Schneider produce rcbos with no neutral fly lead on their acti 9 isobar P DB’s, think the rcbo’s are only single pole tho.
No fly leads on eitherno neutral or no earth?
Because its ours. Long live the RFCBecause we are British and don’t like change and have to do everything differently to the rest of the world
not seen these as yet.No fly leads on either
Isobar P is the first LV distribution board to have a plug-on RCBO (residual-current circuit breaker with overcurrent protection) capability. RCBO neutral and functional earth connections are usually wired into the neutral and earth terminals inside the distribution board, costing significant time by introducing additional wiring. With the new Acti9 Isobar P, installers can simply plug their RCBO directly into the board. This eliminates the need to cut, straighten or dress any excess wiring therefore reducing installation time by half.
See link abovenot seen these as yet.
2 modules is Far too big for some of the domestic CU’s and won’t fit in 3phase DB’sContactum make dual pole RCBO's to international standard which in France, Switzerland and Germany it is a requirement to disconnect the neutral on activation: 40 Amp 30mA RCBO - 2 Module - Contactum - https://www.tlc-direct.co.uk/Products/CPBR402.html
I went with Wylex for that reason, but in my case it is more about ease of testing.2 modules is Far too big for some of the domestic CU’s
Wylex and Crabtree do a single module type which is DP
DP rcbos is definitely a consideration and necessary for that reason but you can have a domestic CU with just a mains switch isolator giving you your DP isolation and just single pole rcbo’s for the final circuits. Same principle for 3 phase, as long as the tails are subject to non movement and enter a ferrous material in a suitable gland etc, and are the insulated and sheathed typeI went with Wylex for that reason, but in my case it is more about ease of testing.
Another difference is in the UK a TT supply with a RCD incomer is relatively rare so you don't usually have to worry about a N-E fault tripping the RCBO and that, if single pole, will not isolate the N fault so the main incomer RCD might also trip.
Not the current, though 6kA is low for a TPN board. It might be the phase barriers are not up to 400V or something, but whatever the reason they are not listed by Wylex as approved.Why not?
If it’s because of them being only 6Ka then they don’t necessarily need to be greater than 6Ka
Something to bare in mind, cheers.Not the current, though 6kA is low for a TPN board. It might be the phase barriers are not up to 400V or something, but whatever the reason they are not listed by Wylex as approved.