A question for testers to settle a debate at work - GN3 & regulation 612.3.1 state that when doing insulation resistance, the CPC/armour of swa MUST be connected to Earth.
Does anyone know why this is please?
 
Because the IR test is between line and CPC/earth - if the CPC isn't connected to anything then you could have a short between line and CPC/earth which the test wouldn't identify.
 
By completing the R1+R2 testing at each point on the circuit during initial verification you are confirming the cpc is continuous and present then you can move on to IR testing , assured that the cpc’s will be included in the test and is not discontinued to give the tester false or incorrect readings.
There is a reason that the testing sequence in initial verification is there and it’s worth remembering that any issues found during IR may mean you have to repeat the previous tests.
 
When you say the cpc / armour connected to earth are you just referring to swa cables and how would it not be connected to earth if glanded to a metal enclosure.
 
The compelling reason,over-rides the regs,as it is a fundamental requisite,of complete and thorough testing.
Out of interest,why do you think,it is necessary?
 
It has been explained but you don't seem to have understood.

You have to have a CPC for the IR test to work.
You need to test the CPC before you do any other test that needs the CPC.

It's like making sure your tester works and your leads aren't broken before you start testing.
 
It's the same idea - if the live is making contact with the armour then an IR test will show that up unless the armour isn't earthed, in which case it'll just liven up the armour to 500v. The test might show you have a high resistance, but then when you energise the circuit the armour will become live.
 
Perhaps the op is getting a little confused and is referring to the requirement to discharge the conductors of an swa to earth following an insulation resistance test. I could be barking up the wrong tree though.
 

Reply to Why Earth before IR testing? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
759
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
748

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
272
  • Question
He is after the four options for 1 and 2 of the multiple choice exam, probably optimistic someone will know this. Your question 3 in incomplete to...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top