stuban

Hi chaps

Just quoted for a job based on a spec which included earthing a metal oil pipe to a new rod at the plastic tank about 15 yards from the house.

The house is out in the sticks but pme. The pipe is not plastic coated that I could see so is there any reason for this? I would think this is a no-no rather than being of any benefit.

I could maybe understand it if the pipe was insulated and the system TT(or is that rubbish) but assuming we bond where the pipe comes into the house is there any situation where you'd earth this pipe to a rod?

Thanks a lot
Stu..
 
It's not very clear your post are you bonding the oil pipe coming into the house , which is a PME earth and then bonding the tank outside of the house with a rod.

If your bonding the pipe going into the house then that is bonding main services as you do with gas and water so pretty straight forward.

As for earthing the pipe at the tank all I can think is that they want to earth the system for when the tanker fills the tank the same as they do at petrol stations.
 
As both above, though in this case I would push for a "proper" PME and want to drop a rod at the MET with a connecting conductor capable of taking full diverted N current and then a bit probably, I would not dream of less than a 16mm tbh.
 
I've not included the rod on our quote because I couldn't find a reason for it. The spec was from the previous quote and what the customer based their spec on.

Agree the bonding is a no brainer but being new to the business wanted to see if I was missing something with the rod at the tank.

Cheers
Stu..
 
True PME mate, also as has been said static.
If the house earth (N) fails then any diverted N current will seek your rod at the tank 1st rather than look to earth through other means, you rod at the MET would also help in reducing diverted fault currents as would the tank rod.
I would say best practice rather than no reason.
 
As both above, though in this case I would push for a "proper" PME and want to drop a rod at the MET with a connecting conductor capable of taking full diverted N current and then a bit probably, I would not dream of less than a 16mm tbh.

to be honest paul, i agree with getting PME, but as for the size of earthing conductor to the rod, it isnt neccesary to use a conductor of that size, unless your RA is very low ie, sub 4 ohms. all IMO
 
johnboy,
The OP stated that the supply is already PME, though, to be best practice PME it should have a rod "at" the MET.
I would put the csa in to help keep the Z low, in the event of a fault current you cannot actually calculate the diverted fault currents so as you said IMO follow the Boy Scouts - Be Prepared!
 
Been working my way slowly through gn8 but skipping to 10.9 "potentially explosive atmospheres" (thanks for the steers) says "..a multiple earthed tn-c-s system are not considered suitable for locations where potentially explosive atmospheres exist"

It also addresses protection against static electricity.

Cheers netblindpaul that makes perfect sense. I'm all for belt-and-braces

Thanks all
Stu..
 
to paul,

i understand what you mean, but the resistance of the conductor will be negligible compared to Ra. As for diverted currents, then ohms law has to apply? id never size a cable for earthing on its limits on a rod, in case ground conditions change for the better, and your fault curents increase.
 
Been working my way slowly through gn8 but skipping to 10.9 "potentially explosive atmospheres" (thanks for the steers) says "..a multiple earthed tn-c-s system are not considered suitable for locations where potentially explosive atmospheres exist"

It also addresses protection against static electricity.

Cheers netblindpaul that makes perfect sense. I'm all for belt-and-braces

Thanks all
Stu..

Stu,
Doubt that you would have an Ex atmosphere around a domestic oil tank and DSEAR does not apply to domestic dwellings only workplaces anyway.
I realise a domestic premises becomes a workplace on times, however, I feel that DSEAR would still not apply!
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Why earth oil pipe at tank?
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
24
Unsolved
--

Advert

Thread statistics

Created
stuban,
Last reply from
stuban,
Replies
24
Views
14,501

Advert

TrueNAS JBOD Storage Server

Back
Top