You could make up a pathological case of, say, a 50W LED flood lamp at the end of several hundred meters of 1mm cable. It meets the VD for its fixed load of around 0.22A, and with, say, a 10A MCB the 1mm cable is overload protected, but it might not trip on a L-N fault in any sort of reasonably time-scale.
Err

That's the stuff I come across sooooo.. often!

Pre covid, a lot of my work was hospitality rebuilds/renovations frequently in the highlands, almost all have long private approach roads with a few led lamps, but hundreds of metres away from the supply.

I would say over 90% have been wired in 1.5mm^2 swa because the load is so small, - even with the small loads the voltage drop is more than allowed, never mind meeting any trip times whatsoever
 
And here was me making it up to show an example!
As you said "bad design knows no limits..."

Although use of the word "design" in these cases would be a new definition of the word!

Just no thought to what was being done at all.

I suspect the swa is the size it is because it's the smallest they could get.

(Two core, poorly installed to boot)
 
Interesting, A while ago I had conduit CPC fail on 2 circuits with 50-150ohm Zs, I pulled through a new CPC for one of them, and for the cooker ran a new bit of T&E as was close to CU.

Although I believe this is the best way to fix it as now has a nice low Zs and meets disconnection time for the MCBs, But in theory if the circuits were on an RCD or upgraded to be on an RCD then could have been left like this as the 150ohms is enough to meet disconnection due to the RCD.

If it was to later have an EICR though I cant imagine many people passing it without a code as the r1+r2 would be high
 
Interesting, A while ago I had conduit CPC fail on 2 circuits with 50-150ohm Zs, I pulled through a new CPC for one of them, and for the cooker ran a new bit of T&E as was close to CU.

Although I believe this is the best way to fix it as now has a nice low Zs and meets disconnection time for the MCBs, But in theory if the circuits were on an RCD or upgraded to be on an RCD then could have been left like this as the 150ohms is enough to meet disconnection due to the RCD.

If it was to later have an EICR though I cant imagine many people passing it without a code as the r1+r2 would be high
This is where experience and common sense kicks in (hopefully)....if such a reading was obtained on a TN system clearly alarm bell should ring despite the presence of an RCD, and if a TT was in place you would hope an experienced person would verify that the high reading was due to the Ra and not a wiring issue.
Experience electricians recognise when a problem exists regardless of the regulations.
 

Reply to Why is a too high zs reading on a circuit okay if it’s protected by an Rcd? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
Replies
3
Views
403
Yes, probably overthinkig, thanks.
Replies
6
Views
605

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top