Why is neutral at 0 volts? | on ElectriciansForums
Discuss Why is neutral at 0 volts? in the UK Electrical Forum area at ElectriciansForums.net
LmarshallSparks
Supporter
Gloucestershire
I’m confused why neutral is at 0v (or close too) in certain situations!
TN-C-S system for this example, no borrowed neutrals or faults! A simple lighting circuit!
Now I can understand that when the circuit is open neutral would be at 0 volts due to it being connected to the earthing conductor and having no line to it! Now let’s say we closed that circuit (turned a light on), I can’t understand why the neutral wouldn’t become 230v
Now I understand most replies will say due to voltage being potential difference we need that difference! However what I can’t understand is now that circuit is closed why doesn’t one of two things happen
1) The neutral becomes 230v
2) The line becomes 0v
Is this due to the extremely high resistance of a bulb or appliance etc using that voltage up, meaning that very few volts remain by the time the current reaches the neutral so it takes the easy path back to the transformer and lacks the power to take any other direction?
Or am I going far too complicated! Is it simply potential difference! The transformer is pushing 230v down the line and the neutral is connected to earth so will always remain at 0v (or close too)
Appreciate any help on the matter!
the entire voltage drop in the circuit is across the load (light in this case) the other parts of the circuit are at zero ohms or close enough to that for there to be no volt drop.
if you were to disconnect the N then it would become live but the lamp would not come on.
Neutral has current but no voltage. Current entering a node must equal current leaving it. As above though voltage is dropped over the load.
If it wasn't, all the pipework in your house etc. would come live via the bonding conductors, this would not be ideal.
The full voltage available (230V) distributes itself along the live supply wire, the load, and the neutral wire in proportion to their individual resistances.
For instance, if the live supply wire was 1 ohm, the load 8 ohms and the neutral 1 ohm, there would be 23 volts from end to end of the live wire, 184 volts across the load and 23 volts across the length of the neutral. There would be no current in the earth wire, so if you connected a meter between neutral and earth at the load end you would measure 23 volts, but 0 volts at the supply end, for a TNC-S supply.
In practice, the supply wire resistances will be much less than 1 ohm and the load resistance will be much higher than 8 ohms for a domestic lamp, but even than there will be a measurable voltage between neutral and earth at the lamp end.
So simply put, the voltage is lost via the load (lamp in this example) so a very small amount of voltage then takes the current back to the combined conductor via the natural?
Reply to Why is neutral at 0 volts? in the UK Electrical Forum area at ElectriciansForums.net
Thanks again, I’m sure I’ll be back with many more questions
In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...