However Im still trying to wrap my mind around why TT needs 4 core and TN-C-S only needs 3 cores. Both will do with 3 phases plus a neutral however its done.

TT needs 4 cores for the 4 live conductors (3x L + N) which would all need to be surrounded by an earthed metal covering or armour.
TNCS does not have a seperate neutral conductor so needs one less core.
 
also, since we touched the subject, if something does pierce the cable, do the DNOs have something to clear the fault or at least fast enough? Im aware of places like Australia where an LV cable fault results in major fireworks as the secondaries are unfused with the primaries being fused at 2x the trafo's primary full load current.

Yes they do have something which will clear the fault, usually fuses or ACCBs, which clear the fault in the required time. Bearing in mind they have their own standards to work to with regards operating time for such protection.

As for Australia I couldn't possibly comment, and don't see how it is relevant
 
TT needs 4 cores for the 4 live conductors (3x L + N) which would all need to be surrounded by an earthed metal covering or armour.
TNCS does not have a seperate neutral conductor so needs one less core.



Wait, why would TT need a dedicated neutral conductor? If the armor on a TN-C-S supply serves as a neutral, then why cant it for TT?
 
Yes they do have something which will clear the fault, usually fuses or ACCBs, which clear the fault in the required time. Bearing in mind they have their own standards to work to with regards operating time for such protection.

As for Australia I couldn't possibly comment, and don't see how it is relevant

If the conductors do not have fuse protection, an outer armor does nothing.
 
Wait, why would TT need a dedicated neutral conductor? If the armor on a TN-C-S supply serves as a neutral, then why cant it for TT?

Because the neutral in a TNCS is a CNE (combined neutral and earth) so is one conductor serving both functions with strict requirements for the number and impedance of N-E connections made via earth electrodes along the distributing main.
In all other systems N and E are seperate conductors and are not permitted to be connected after the N-E link at the substation/transformer.
 
Because the neutral in a TNCS is a CNE (combined neutral and earth) so is one conductor serving both functions with strict requirements for the number and impedance of N-E connections made via earth electrodes along the distributing main.
In all other systems N and E are seperate conductors and are not permitted to be connected after the N-E link at the substation/transformer.


No connection to earth occurs in TT either at the customer's premises. A PME incomer will happily serve a TT supply.
 
Ok, maybe I did not clarify. By TN-C-S I meant the incomer which is pure TN-C. A pure TN-C incomer can go either TN-C-S or TT.

How are you defining the 'incomer' as its a bit ambiguous.

That is still irrelevant to the point, your op was regarding the advantage to the DNO of converting their networks to TNCS supplies universally. My answer being the cost advantage as TNCS is cheaper for them.
 

Reply to Why TN-C-S? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
669
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
Yes, for example: https://kingsmillindustries.com/product/km2-20-10-sc/ However, the reality is the L-N-E style are far more useful in general as...
Replies
2
Views
1K
M
  • Article
S-traps self Syphoning I watched a video and it went in about S-traps self spyhoning after discharge and said they were band in the USA. This...
Replies
0
Views
119
Matt0029
M

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top