Why are UK DNOs TN-C-Sing everything? Why does that hold more advantage then TT?
https://www.youtube.com/watch?v=JRHyqouJPzE
https://www.youtube.com/watch?v=JRHyqouJPzE
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Why TN-C-S? in the UK Electrical Forum area at ElectriciansForums.net
However Im still trying to wrap my mind around why TT needs 4 core and TN-C-S only needs 3 cores. Both will do with 3 phases plus a neutral however its done.
Really?Hows so? TT requires the same amount of wires.
also, since we touched the subject, if something does pierce the cable, do the DNOs have something to clear the fault or at least fast enough? Im aware of places like Australia where an LV cable fault results in major fireworks as the secondaries are unfused with the primaries being fused at 2x the trafo's primary full load current.
TT needs 4 cores for the 4 live conductors (3x L + N) which would all need to be surrounded by an earthed metal covering or armour.
TNCS does not have a seperate neutral conductor so needs one less core.
Really?
Yes they do have something which will clear the fault, usually fuses or ACCBs, which clear the fault in the required time. Bearing in mind they have their own standards to work to with regards operating time for such protection.
As for Australia I couldn't possibly comment, and don't see how it is relevant
As the neutral is referenced to earth it also acts as a cpc. If you applied this to TT it would become TNCS!Wait, why would TT need a dedicated neutral conductor? If the armor on a TN-C-S supply serves as a neutral, then why cant it for TT?
Wait, why would TT need a dedicated neutral conductor? If the armor on a TN-C-S supply serves as a neutral, then why cant it for TT?
If the conductors do not have fuse protection, an outer armor does nothing.
Because the neutral in a TNCS is a CNE (combined neutral and earth) so is one conductor serving both functions with strict requirements for the number and impedance of N-E connections made via earth electrodes along the distributing main.
In all other systems N and E are seperate conductors and are not permitted to be connected after the N-E link at the substation/transformer.
No connection to earth occurs in TT either at the customer's premises. A PME incomer will happily serve a TT supply.
Yes it would, and does in some places, but is irrelevant to the point as it would still be the same TNC distribution side as a TNCS supply not a TT distribution
Ok, maybe I did not clarify. By TN-C-S I meant the incomer which is pure TN-C. A pure TN-C incomer can go either TN-C-S or TT.
This is a video of an 11kva cable strike.
I think they must have something to clear faults?
https://m.youtube.com/watch?feature=youtu.be&v=bpX3VHKAKak