Planning my consumer unit change ready for my assessment in a couple of weeks. Looking at the board - and note i've not investigated any further i seem to have 2 40amp CB's labelled Shower front and shower back. Both are rated 40amps. Now i only have one shower and i cant see there ever being a shower in the front of the house anyway so im not sure if the labelling Front and back refer to the actual location

Is there any reason why a shower with pull cord isolator would be wired with 2 supplies ?
 
I would investigate this as a matter of urgency before your assessment, switch 1 breaker off at a time to see whitchbreaker feeds your shower. Once this has been proven the find out where the other cable goes, has you House ever had two showers? Do you have a supply to an external building? could be someone in the past has used one of these supplies to feed a shed or Garage, just putting possibilities your way, let us know what you find please, sounds interesting.
 
I'd put money on one being a redundant shower feed. As Pete says a thorough investigation is the way forward, especially as a precursor to the board change and the impending assessment.
A nosey in the loft may also reveal hidden treasures in the form of disconnected shower supplies.
 
The history of the build is. House built early 80's. Extension with electric shower and board change completed 2005. So 1 supply cable is white and 1 is grey as you would expect. Just looking for the paperwork for previous board change and will complete a full set of tests tomorrow to compare.
 
The history of the build is. House built early 80's. Extension with electric shower and board change completed 2005. So 1 supply cable is white and 1 is grey as you would expect. Just looking for the paperwork for previous board change and will complete a full set of tests tomorrow to compare.
 
Many people on this forum do this type of work most days and will often encounter this and more don't want to be rude but have to agree with above post if being assessed to join a scam/scheme what will you do if you pass and are in a customers house doing consumer unit upgrade.
 
Many people on this forum do this type of work most days and will often encounter this and more don't want to be rude but have to agree with above post if being assessed to join a scam/scheme what will you do if you pass and are in a customers house doing consumer unit upgrade.
Like I said earlier in thread, I will take a look as anyone would in this situation. Let's be honest technically any domestic electrical work or commercial for that matter isn't really that difficult. Working out what others have done in the past is
 
test both supplies, the one that has the worst test results, pop that behind the wall

no point over complicating this problem, shower needs 1 supply so use the best cable and disconnect the other 1
 

Reply to Why would my shower have 2 supplies in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
397
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
986
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Being pedantic, the Crabtree 50A cooker switch is a 4500/1, which has 'cooker' printed on it. For a shower, you require the 4500, which is the...
Replies
3
Views
341
  • Question
Better off with the click prw213 as it has twin screw termination.
Replies
9
Views
995

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top