I'm confused as to why the below happened.

1) isolated downstairs lighting circuit, kitchen light still works

2) isolated kitchen light and provided an earth for the diy metal light switch (after seeing the lounge switch didn't have one either)

3) after sorting all switches energised the circuit, MCB tripped. When MCB back on the kitchen light wouldn't switch OFF. Traced fault to loose line in kitchen switch. Sorted and all now fine.
 
I've been dealing with an EICR for LABC regularisation the last few days (some pics to be posted) and one of the things I checked, based on the fact I had CPCs connected on different circuits within the installation was actually systematically turn on one circuit at a time and check for the presence of supply at the load terminal of each circuit just to make sure I had no interconnected circuits. Also did IR between many of them to double check.

Could be a mixup like that.
 
I initially thought it must be interconnected circuits but the fact it then blew the correct MCB made me think otherwise??
Couldn't be incorrectly labelled as it tripped correct MCB.
@hightower, that could explain it as could Richard's suggestion.
 

Reply to Why would this be? And I've got the 20 char thing too?? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
393
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
978
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top