What if your Zs is too high yet your trip times comply?
Zs is less or equal to Uo/Ia and Ze = Zs + (R1 + R2)
i still belive that a mechanical earth ie conduite trunking is a better fault path than 2.5 4mm cpc on lighting and power circuts it was ok 20 years ago and i still get lower readings wen i test itThe lower the Zs then the higher the fault current, the higher the fault current the faster the protective device will operate.
i still belive that a mechanical earth ie conduite trunking is a better fault path than 2.5 4mm cpc on lighting and power circuts it was ok 20 years ago and i still get lower readings wen i test it
i always test both any wayc pc and mechanical i disconnect all metal work fly leads etc take a reading on the cpc then re connect fly leads metal work and test again so wat is the point in running cpcs in a conduite trunking insatalltionProbably because you are getting parallel paths
What if your Zs is too high yet your trip times comply?
For instance say on a consumer unit upgrade, and what can be done to rectify this?
i always test both any wayc pc and mechanical i disconnect all metal work fly leads etc take a reading on the cpc then re connect fly leads metal work and test again so wat is the point in running cpcs in a conduite trunking insatalltion
The point is that steel conduit and trunking is liable to corrosion at joints and is very dependant on a high standard of workmanship for good electrical continuity. Thus in the long term a mechanical cpc may be subject to a deterioration in the continuity.
well thats why its all galvanised so it does not deteriorate over timeThe point is that steel conduit and trunking is liable to corrosion at joints and is very dependant on a high standard of workmanship for good electrical continuity. Thus in the long term a mechanical cpc may be subject to a deterioration in the continuity.