I live in Phnom Penh, Cambodia and people die here regularly by electrocution. There is no earth wiring in the buildings, just live and neutral.
I am a member of an expats forum and the question arises: Will using an RCD device offer any protection at all?
I understand RCD's will go off with any leakage and that may have to include the human being the earth. At the moment my apartment has 8/16/32 amp circuit breakers and nothing else.
I can buy plug-in type RCD units to go between an appliance (like the washing machine) and the wall socket. Will this offer any protection even it is me being the earth! 😱
Short answer is yes it will give you added protection from death by electrocution
if more than 30mA passes through you then the rcd will turn the power off.
Is that on the basis that I will be the earth?
Will an RCD give an early warning that an appliance is already dangerous, i.e. as soon as I plug it in via the RCD it keeps tripping the RCD?
In short, the rcd compares live and neutral currents and trips the power if there is a difference between them
it can’t tell where the current is going other than if what flows out of the live is returning via the N
it will not detect over current.
the problem is, the off button or test button on the rcd will use the earth to create a small imbalance between the L and N to test the internal circuits of the rcd.
if you have nothing connected to the earth terminal then this will not work.
the rcd should still work but you will be unable to test it.
Very interesting. I am going to have some sent over form the UK soon so I will get them to test them first then send them.
Thanks for your time.
Many RCDs use a small resistor to push a small amount of current between L-N when you press the test button, no earth required to test. To Op, having an earthing system will enable breakers to trip due to short circuits to earth and will protect the building and reduce chances you touch something live like the casing of a toaster. If there is no earth then yes you become the path, but this is no different to many situations where live is directly touched by a person even if they have an earthing system, so yes its much better having RCDS than not . You can get a single up front RCD that goes at the beginning of your system. Make sure the RCD is designed for your countries mains voltage and frequency.
Without knowing the details of the supply system we can't say for certain whether an RCD will work or not.
It will depend largely on whether the neutral point at the substation transformer is actually connected to earth or not, if it isn't then the RCD won't work (although you shouldn't be able to get a shock to earth in this situation)
Nice to have you back........
What others have mentioned without going into detail is how the system would work with an RCD and faults.
Unless it's a very small system, then I would suggest that the combination of leakage, capacitance, and faults in various parts will mean that it's highly unlikely to behave as a true floating system would be expected to - i.e. even in the absence of faults it would be possible to get a shock.
But back to the OP.
If your appliance develops a l-E fault, then without any earth connection the casing will become live - it will continue to work normally (assuming the fault doesn't itself interfere with operation), but will be dangerous to touch. Clearly some of these appliances will be within touching distance of extraneous earths, such as you'd find with a metal water pipe that's buried in the ground. So if you are leaning on the sink when you touch the (faulty) washing machine then you'll get a shock from the full mains voltage - but it is unlikely that the current will be sufficient to trip any breakers/fuses.
If you have an RCD in the circuit, then the fault in the appliance will still not trip anything - it'll sit there with a live case, and still working. But when you touch it, at the same time you have a conductive path to earth, then the RCD will detect the imbalance (not everything going out the live wire will be coming back on the neutral wire) and trip - hopefully quickly enough to prevent the shock being fatal.
But what if you aren't touching a sink that's earthed via the pipes ? Well then the question is how well earthed are you ? There is always some linkage via capacitance, but if you are in dry shoes & socks, on a dry floor, you might not get a shock - just a bit of a tingle, and not enough current to trip the RCD.
I recall many years ago I worked on a farm (I also knew fairly little about electrics and safety, and had no test equipment) - this was before RCDs were common. We had a free-standing water heater, and started noticing a tingle when we touched it. We were always wearing rubber wellies, so even though we were stood on a wet floor which would provide a fairly decent earth, it did no more than give us a tingle. When I looked, the contacts for the earth pin in the socket (an old 15A round pin one) had been bent - so I squeezed them back together, and when I switched on, one of the elements went with a bang.
So yes, adding one or more RCDs will vastly improve your personal safety.
It could be just one in your supply - but it's generally advised that you split the installation across at least two. Having multiple RCDs, each protecting part of the system, means that there is less leakage current so nuisance trips are less likely - but also means that if one does trip, you still have some circuits working.
At a pinch, using a plug in RCD will give some protection - but only to faults with whatever is plugged into it.
When picking an RCD, be aware that some (notably many of the ones built into RCBOs - that's a combination fo RCD and the overload function of your existing breakers) have a white or cream wire coming out that needs to be earthed. Avoid these, there are plenty of RCDs that don't have this.
Also avoid any time-delayed versions - these won't trip fast enough to stop you getting a fatal shock. They are used (simplification) where it's required to protect part of the wiring system (e.g. a sub main), while still providing discrimination with non-delayed RCDs downstream. Without the delay, a fault on any downstream circuit would trip both the RCD on that circuit and the one further upstream.
For safety, it would be a good idea to add earthing to all circuits - though I realise that's going to be impractical for some (particularly rented places), and an upheaval where it is practical.
But the principle of the majority of electrical system in residential settings (it can be different in a commercial/industrial setting with trained staff monitoring things) is that all exposed conductive parts are earthed - so that if there's a fault, the current that will then flow will blow a fuse or trip a beaker, thus disconnecting the supply.
There is also the idea of double insulated appliances where there is extra insulation so that a fault between the live supply and any exposed metalwork is made very unlikely - but you won't find washing machines built to that standard.
And of course, whatever you or the others on the forums decide to do, you'll need to find out what the local rules/regulations are. For example, in many areas, only licensed electricians are allowed to do any electrical work.
So in a curious moment I've just scan read the Cambodian electrical regs (something not actually so unusual for me given my global work scope). An interesting beast - seems to take bits here and there from other nations but doesn't really join the dots very well between them all. The MV transmission system and my interpretation of the LV installation system (230v, 50Hz) is that it's meant to be what we'd know as IT - there is a specific clause that implies everything should be insulated from Ground.
However, in another section which seems to have been lifted from BS7671 of a few years back it talks about making TT/TN systems.
What there IS, though, is this....
If the appliance is not connected to earth then the RCD will not have any earth leakage current to detect, until your body provides a path when you touch it. So the RCD with no earth won’t trip.
This applies in many cases. If the faulty appliance is Class 1 but the earth connection has come adrift, then it may sit there at full mains potential until someone touches it, and the same applies to Class 2 equipment with eternal metal parts, where the double insulation has failed (or nigh impossible to comply with when installing, in the case of many imported light fittings).
If both sides of the supply are truly floating, then a fault of this kind shouldn't be dangerous, but capacitance, leakage and the possibility of an undetected existing fault elsewhere makes this something I wouldn't rely on. It won't matter that a 30mA RCD won't trip, as it will mean that the fault current flowing through your body is less than 30mA, so shouldn't be fatal, (usually).
That's not how the test button works on any RCD that I've encountered. The test circuit takes current from the 'in' side of one pole and the 'out' side of the other, so the 30mA that flows when the test button is pressed only flows through the sensing coil on the side where the test current is taken from the 'out' pole.
This arrangement does not rely on any earth connection, allows the RCD test circuit to operate whichever end is used for supply and load, and disconnects the test circuit as soon as the RCD trips, allowing the resistor in the circuit to be rated at much less than the 7W it would otherwise need to be rated at in case someone held the test button in.
Welcome to the forum by the way!
Also, a tip for the speed readers - the above comment is one that people need to read carefully in the context of the direct question above it (about whether an RCD provides any early warnings of no earth connection) as opposed to the original question in this post about whether an RCD improves safety if there's no earth connection at all.
Agreed! I failed to do the above, which is why my answer to the question has been edited into rambling gibberish.
International distribution systens are fascinating, and completely dispel the myth that Brit is best, too. For example I'm currently in Australia, in basically a Brisbane city suburb. Walking down the road and I realised when glancing at the poles that the same pole is carrying both HV and LV - Conventional delta HV on top and then intermittently it drops down via a TX onto the LV lines and appears as 3PN. Earthing (that I've seen, anyway) is TT. A simple idea that must save on costs massively whilst delivering constancy over long distances.
The power providers in France leave the earthing arrangements to the home owner so TT systems are the norm, most electricians carry large SDS drills for that purpose.
Australia's LV distribution is almost exclusively PME/TNCS, here called MEN (Multiple Earthed Neutral). You'll find very few TT systems here.
But isn't there still a leakage / loss of current if the appliance develops a ground fault (i.e. the active/live wire touches the appliance chassis/casing)? Therefore, this will create an imbalance of current between Live and Neutral and therefore the RCD will still trip?
Only if the unearthed appliance is in contact with the general mass of earth, which is by no means certain, since many appliances sit on rubber or plastic feet.
Not if it is not connected/isolated from earth. Live will touch the casing, have no where to go and not create an imbalance.
Yes, there's a good chance that your body will provide a path to earth and imbalance the currents, with the result that the RCD trips.
This will probably save your life, but it will still hurt.
Can you really say a 'good' chance? If you see post number 9 your body will only provide a pathway to earth if the neutral point of the transformer is earthed. I have absolutely no idea if this would be common practise in the OP's country.
I suppose it couldn't actually do any harm by using a plug in RCD. It would either not work, so you're no worse off, or it would work and probably safe your life. So I guess it's a good idea. However, by using an RCD you may feel a sense of security and take greater risks!
Ok.
But this is what I still don't get (apologies for my ignorance)---> your responses imply that the current is still flowing to Neutral? But how is that possible if the current has left the intended live-neutral loop?
Note: My logic / assumption is that if a Live wire touches a metal chassis, then that means it is no more connected to neutral. And if it’s not connected to neutral, then there’s no way for the current to flow back to neutral (hence my reasoning why the RCD will trip). What am I missing here?
Ok.
If the connection has broken inside the appliance and contacted the chassis instead, then with no neutral return path there will be no current and the appliance will not work. The casing will be live and if someone touching it completes a path to earth/neutral they will get a shock, but the RCD will not automatically trip.
This is one reason why if e.g. a light or heater doesn't start when you plug it in and turn on the power (assuming its own power switch is on) then it should be unplugged before being examined as a broken internal wire may be touching the casing.
I entered this thread because video below states that when a Live wire touches a metal frame there will be current leakage causing the RCD to trip. No earthing of the metal frame, no person touching the frame. RCD still trips.
This video seems to contradict the initial responses I received above, which states the RCD will trip when a ground fault happens but only if the metal frame is connected to earth.
Confused as ever....:(
starts at 3:00
There is a few ifs and buts here. If the frame is not earthed, say it is floating in the air and completely isolated then there is nowhere for any current to go and as such the RCD shouldn't sense an imbalance.
Another scenario, again the frame is not earthed by way of the electrical system but has a tenuous contact to earth. For instance a washing machine sitting on a damp floor which is likely to allow leakage to flow hence you get an imbalance.
You're pretty adamant there won't be any current leakage as the current travels through the body of the frame....not saying you're wrong, just interesting to hear different viewpoints.
Follow on question ---> so how does the current make its way back to neutral from the frame?
If it has no possible return to earth no current will flow. If I touch a live wire to a metal spoon on a rubber mat there is nowhere for any current to go, this is the same scenario.
Sorry, I wasn't being clear enough ---> I'm not talking about the current going back to neutral via earth. I'm saying how does the current that is now buzzing around the metal frame/body make its way back to the RCD?......because the point is if we say the metal frame is not earthed AND we say there is no imbalance in current, then that must mean the current is making its way back via the circuit's neutral wire....correct?
As mentioned before, the DNO supply transformer is expected to have a centre point Neutral which is then referenced to Earth at the Substation and in some cases along the route to the home/businesses. Any conducting surface like a toaster casing that has become live, if the toaster is earthed at the home, the current will either flow along the home earth to the DNO earth or Earth Rod and make its was back to the Substation to complete the cct. As this is a long path/highish resistance path it may not trip a breaker or blow a fuse but just sit there. Along comes a human , touches the case and creates a parallel cct through the human body to the floor or if touching an earthed component like a radiator or kitchen tap a highish current will flow through the human. If an RCD was in cct, it would see current down the live and not coming back to the neutral through the RCD as its been diverted through the human to a parallel path back to the substation, hence it can trip if the impedance is low enough.
Perhaps you're confusing current and voltage. There will be a voltage at the metal frame, but in order for a current to flow anywhere there needs to be a complete circuit, either back through the neutral to the transformer, or back through the general mass of earth to the neutral point of the transformer.
Current does not 'buzz around', it is the flow of electricity in a conductive material. If there is no path for current to flow, there is no current.
What "current buzzing around the frame" ?
Are you familiar with Kirchoff's 1st (or Current) Law ? Put simply, all the current going into/out of the device (via whatever routes) must sum to zero. If there is no path to ether from the frame (lets say it's sat on a perfectly insulating surface and has no earth connection) then there can be no flow of current between frame and earth. If the live supply wire comes free from it's terminal and touches the frame then two things happen :
1) The supply current will stop. There's no longer a path from live to neutral via the device load, and no path to earth from the frame, therefore when you apply Kirchoff's law, there can be no current in the live. No current in the neutral, no current in the live, therefore no current imbalance and the RCD will not trip.
2) The frame will become live. Simply, there's no a connection from the live supply to the frame, so the frame will be sat there at mains live voltage.
......because the point is if we say the metal frame is not earthed AND we say there is no imbalance in current (meaning the RCD won't trip), then that must mean the current is making its way back via the circuit's neutral wire....correct?
No, as above, there will be no supply current - it has nowhere to go to.
Remember, the supply does not "push current" through the loads, it forces a voltage onto the loads, the current is drawn according to the supply voltage and load characteristics. That's a common misunderstanding - people thing that you cannot use (say) a 2 amp power supply to for a device that only draws (say) 1/2 amp, they believe that somehow the 2A supplyt will force 4 times the current through the device and fry it. Assuming the voltage is the same, the device will simply draw it's normal 1/4A from the supply.
Now, there can be a discussion as to whether a large device sat on an insulating mat really will pass zero current to earth. In practice, the frame, mat, and floor/ground will form a small capacitance which in the presence of an AC voltage will pass a very small current. But for this discussion that current will be small enough to ignore.
Phnom Penh Cambodia
All Other Countries (This Is English Speaking Website Only - WE don't mind Google Translate Users :)
Other
If other, please explain
Amateur in need of help
Business Name
No Company
Will an RCD offer any protection in a building with NO earth circuit?
AmatuerinCambodia,
GeeGee50,