P
PC Electrics
Here's a clue:
RCD = supplementary protection......
RCD = supplementary protection......
But if the circuit is on an RCD anyway, the Zs measurement becomes irrelevant
The way I see it is
R1 + R2 + Ze = Zs
The R1 may have a very high resistance perhaps through a loose connection or faulty accessory that may cause a fire if the overheating is allowed to continue un noticed
The presence of an rcd will not help if the zs of the circuit is not checked and just assumed to be under the maximum for the rcd
If the standard test is carried out this would be noticed
So sorry to take the opposing view but I still think the test is relevant
Ok chaps
just watched a joint NICEIC/Megger DVD on intitial verification
They state on there that where circuits are RCD protected, the Zs reading need only be taken with a low resolution meter capable of measuring 1667 ohms
I also have in front of me a copy of "Guide to the Wiring Regulations BS7671:2008"
published by no less than the ECA
Page 63 has the following quote under the heading "Irrelevant ELI specification"
"A common source of misunderstanding is that of either specifying or measuring values of ELI where the circuit also has an RCD fitted. ELI measurement under these circumastances is a futile exercise. The circuit will have been checked for continuity, and this is what is needed, together with, of course, functional checks of the RCD...........and for clarification, circuits with RCBO's do not need to meet the specified ELI values"
So back to the original post - will Zs values be irrelevant under the 17th edition? (for RCD protected circuits)
Well I think they will
NICEIC think they will
Megger think they will
The ECA think they will
and for information, the IET often adopt the ECA's reccomendations
*shakey takes a bow*
Hate to say i am right chaps, but, ........erm........point proved i think![]()