I was watching an electrician wire a room stat and was unsure how it worked and he wasn't to inclined to tell me how it works,
from what i can see he wired 2.5 from boiler spur then a 1.5 3core and earth to a room stat from boiler... is this correct?
 
A mechanical roomstat works by the use of a bimetallic strip operating a switch, the temperature set point is adjusted by applying varying pressure to the switch using a cam or similar setup.

From an electrical point of view it is a switch which operates at a set temperature
 
I was watching an electrician wire a room stat and was unsure how it worked and he wasn't to inclined to tell me how it works,
from what i can see he wired 2.5 from boiler spur then a 1.5 3core and earth to a room stat from boiler... is this correct?
if the stat. requires a N, then a 3 core/E is the correct cable to use.
 
Why would a trainee ask a trainee how something is done?? you would ask someone with experience..

The trainee section is an area where access is restricted to genuine trainees and experienced members who have made a commitment to help the trainees without making negative comments, unhelpful remarks, Mickey taking etc.

In the general forum a trainee will be treated the same as everyone else and suffer some harsh banter and Mickey taking for asking basic questions, they will also receive bad advice from people who do not recognise the limits of their own knowledge or will present their opinions as fact.
 
The trainee section is an area where access is restricted to genuine trainees and experienced members who have made a commitment to help the trainees without making negative comments, unhelpful remarks, Mickey taking etc.

In the general forum a trainee will be treated the same as everyone else and suffer some harsh banter and Mickey taking for asking basic questions, they will also receive bad advice from people who do not recognise the limits of their own knowledge or will present their opinions as fact.

Thank you for your help.
 
You should always wire roomstats in 3 core in case the stat is changed in the future and requires a neutral. Pester the bloke to explain it to you.
 
You should always wire roomstats in 3 core in case the stat is changed in the future and requires a neutral. Pester the bloke to explain it to you.

That's what the cpc is for..... convert to switch live when needed (well, that's what my plumber mate told me). Don't you kids learn nothin in college!!
 
To answer your question; YES, 3 core+CPC.
Live, switched live, neutral as some stat have a small heater built in as well as a Neon, which will need a neutral. The CPC may not be required as most modern stats are double isolated, but is good practice in case a class 1 is fitted in the future
 

Reply to Wire Boiler & room Stat in the Central Heating Systems area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
841

Similar threads

I have just looked at the wiring diagram on line and there are a lot of internal links which if in the wrong terminal could put 230 volt onto...
Replies
10
Views
811
S
  • Article
Electrician Boiler Fault Boiler Fault I’m hoping someone can help with this boiler problem. Couple have just moved into a house that has a Grant...
Replies
0
Views
239
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top