The width of the timber is ~95mm. On top of that, there was a 12mm or 15mm plasterboard, either side of the frame. However, that lower beam was drilled at a really funny angle, certainly not in the middle.

View attachment 47484

View attachment 47485
looking at that pic. those holes must have been done by a plumber who failed to go to specsavers.
 
even if >50mm deep, cables should still be run in prescribed zones. those cable don't.
Hi - completely agree that cables should be located in the zones and for some reason this Installer seems to have gone out of their way to not use them - plenty of corners for them to've picked from.

Reading 522.6.202 opening sentence gives the zone exemption if >50mm they may be relying on (?).
 
You may be able to argue successfully that the cables should be re-installed properly. If successful you have the problem they will send the same idiots operatives who put them in to "correct" it.
 
They probably wasn’t expecting the home owner to come along and demolish that storage cupboard. In most new builds you can’t decorate or make alterations within the first 12 months or so.
 
@Fitzy. Is that so they can do the snagging lol.

Yes, usually. Everyone I know who’ve moved in to a brand new home, haven’t been able to decorate for at least 12 months and not been allowed to hang anything on the walls with nails etc for the first 3-6 months. So I guess knocking down a built in cupboard might fall under those terms as well.
 
What’s your intention for the cupboard - it’s not like it has a floor or anything!
It’s technically the airing cupboard but without the immersion of old. Lots of people put a tubular heater in there and store towels etc.
I've never thought of recommending a tube heater in there :eek: good shout
 

Reply to Wire in the in-built wardrobe's wall vs regulation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
675
  • Question
I have to agree with littlespark stating that the wires should be absolutely cut loose at the fuse or breaker to make it safe. The heaters should...
Replies
2
Views
765

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top