devonsparky

Just a quick one

I'm wiring up a hot tub tomorrow (yes, on a Sunday !) know I shouldn't transport a PME earth to the installation.
The house is out in the sticks and on a TT ................ my query is, would you still put an earth electrode locally to the hot tub or would you rely on the main earth ?
 
Hot tub is outside ....... It is rated at 43.5A so I'm putting it on a 1 way board (Main SW 63A RCCB 30mA + 50A MCB) - 10mm SWA
Ze (TT) is 111ohms

Just curious to ideas on whether anyone would also earth electrode at the rotary isolator for the hot tub?
 
It is almost always better to link the earth electrodes on TT systems, ie ...the more rods on the system the better. This can be achieved by the SWA of your supply cable as a last resort, but better if you include a separate core in your cable to take back to the MET...

What is the hot tub sitting on, ...Grass, concrete or slab patio, Wooden decking?? If it's sitting on grass or concrete patio, then i would want to see a much better value than the existing 111 ohm Ra...
 
id earth from new mcb/rcbo enclosure....... would i have to pipe to my eaqrth rod is what i dont know, but i wouldnt do this job.. good luck

- - - Updated - - -

i know mechanical protection from regs and all but just cant picture it and never installed an earth rod yet
 
id earth from new mcb/rcbo enclosure....... would i have to pipe to my eaqrth rod is what i dont know, but i wouldnt do this job.. good luck

i know mechanical protection from regs and all but just cant picture it and never installed an earth rod yet

Why would you Not give the earth cable mechanical protection, surely you wouldn't leave it underground without any protection, .....would you??
 
I've chopped through an SWA a few times with my spade. Thought it was a tough tree root.

What I'm saying is EVEN armoured cable isn't numpty proof. Especially one thats frothing at the mouth with a crazed look in his eye with a Steel spade
 
On my hot tub I had a small distribution actually inside the hot tub (manufactured like this) I took a earth spike to that board, and got it down to 13ohms, also I think your ok to supply with pme if you also get an earth rod with resistance bellow 22ohms locally

Also remember to take your swimming shorts to test it!
 

Reply to Wiring a hot tub on a TT system in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
352
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
901
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thanks for that guys I was more thinking about difference in potential between the tub and wet paving flags . The tub is plastic . But it’s the...
Replies
7
Views
1K
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
799

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top