What is the Kw ratting of the hot tub?
THe tub is 3Kw
3 Kw = 13A + a couple of lights!!!!
Install a none rcd DB in the house, run 4mm SWA from it to the hot tub protected by a 20A MCB. IP ratted CU at the hot tub with 30mA RCD, 16A MCB for the hot tub & 6A MCB for the lights, job done.
The hot tub is 32 amps, the heater is 3Kw, it has 85 jets and water line spot lights, the pumps are 2x 2HP and 1x 3HP.
the supplier demands its RCD protected and demands a rotary switch as that's where they will connect their wires up.
ok let me rephrase the question.
What is the total load of the hot tub? Once we know this we/you can work out what size cable is needed and what size OPCD to install.
Circ pump 750watts
air pump 700 watts
3Kw heater
1x 3 HP pump
2x 2 HP pump
That is all I can find on it,
thanks for The pacience Paul :)
It is advertised at 32A. Google the tech sheet for this model and take it from there. If not just use 6mm 3 core swa and install it as above.
... the Earth at the house is TT
...Install a none rcd DB in the house, run 4mm SWA from it to the hot tub protected by a 20A MCB. IP ratted CU at the hot tub with 30mA RCD, 16A MCB for the hot tub & 6A MCB for the lights, job done.
Looks like the distribution circuit will require RCD earth fault protection unless the Zs is low enough (unlikely).
I would suggest the whole job is reconcidered myself after the latest info from the OP.