TPES

Not that long ago I supplied power to a portacabbin, it was fed from a 3 phase panel in a close by building.

I TT'd the cabbin/site office, there is a small single phase sub board in the cabbin.

Now there is going to be 2 x metal storage containers placed next to the portacabbin for storing materials ect,

The 2 x containers want to have 1 x light & 2 x sockets in each..

My question is, is it ok to use the TT earth rod for the cabbin to earth the 2 containers? Or does each container need it's own rod? There all next to each other.

Also what wiring method would you use for this tempory install, there steel containers and will be there for around 6-8 months
 
Presumably you will supply the two containers from spare ways in the office portacabin in which case use the existing rod....Plastic conduit wiring system in the containers.....dont forget to bond the steel containers.
 
we export the earth from the supply when we wire temporary containers - we also wire in plastic conduit inside.

as a precaution against stupidity, we leave 5 meters of SWA on the roof of each container between termination points, in the hope that if someone tries to move it for any reason and we are not around, they'll see the cable before they just lift the container and rip the installation apart.
 
we export the earth from the supply when we wire temporary containers - we also wire in plastic conduit inside.

as a precaution against stupidity, we leave 5 meters of SWA on the roof of each container between termination points, in the hope that if someone tries to move it for any reason and we are not around, they'll see the cable before they just lift the container and rip the installation apart.

Now that is a sensible precaution
[ElectriciansForums.net] Wiring a temp container?


One slight doubt though,is 5 meters enough length for the idiots brain to process the message before the Doh :)
 

Reply to Wiring a temp container? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
614
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

Ask your electrician when they do a site visit as to what is required they can also notify the installation to Building Control under Part P of...
Replies
1
Views
529
I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
477

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top