Not that long ago I supplied power to a portacabbin, it was fed from a 3 phase panel in a close by building.

I TT'd the cabbin/site office, there is a small single phase sub board in the cabbin.

Now there is going to be 2 x metal storage containers placed next to the portacabbin for storing materials ect,

The 2 x containers want to have 1 x light & 2 x sockets in each..

My question is, is it ok to use the TT earth rod for the cabbin to earth the 2 containers? Or does each container need it's own rod? There all next to each other.

Also what wiring method would you use for this tempory install, there steel containers and will be there for around 6-8 months
 
Presumably you will supply the two containers from spare ways in the office portacabin in which case use the existing rod....Plastic conduit wiring system in the containers.....dont forget to bond the steel containers.
 
we export the earth from the supply when we wire temporary containers - we also wire in plastic conduit inside.

as a precaution against stupidity, we leave 5 meters of SWA on the roof of each container between termination points, in the hope that if someone tries to move it for any reason and we are not around, they'll see the cable before they just lift the container and rip the installation apart.
 
we export the earth from the supply when we wire temporary containers - we also wire in plastic conduit inside.

as a precaution against stupidity, we leave 5 meters of SWA on the roof of each container between termination points, in the hope that if someone tries to move it for any reason and we are not around, they'll see the cable before they just lift the container and rip the installation apart.

Now that is a sensible precaution
icon14.gif


One slight doubt though,is 5 meters enough length for the idiots brain to process the message before the Doh :)
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Wiring a temp container?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
5

Thread Tags

Advert

Thread statistics

Created
TPES,
Last reply from
mogga,
Replies
5
Views
8,743

Advert

TrueNAS JBOD Storage Server

Back
Top