All concealed cables require some form of additional protection, and have done so for a number of years.
One method is to bury the cables at least 50mm from the surface.
If that is not possible, then an option is to use cables which incorporate an earthed sheath such as Flexishield or SWA.
Another method would be to run the cables inside earthed conduit or trunking.
You could provide mechanical protection, sufficient to prevent penetration by screws or nails.
The final option is to install the cables within prescribed zones often refered to as safe zones, and provide 30mA RCD protection.
From the OP, it would appear that the cables are not being run in safe zones, so 30mA RCD protection is not an option.
Unless the cables used incorporate an earthed metallic sheath and as it appears that no earthed conduit or trunking is being used.
The only options available are mechanical protection or installing the cables at a depth greater than 50mm.
Seems to me that an awful lot of plasterboard would be required to provide a depth of 50mm.
Some plasterboard is manufactured with insulation fixed to the back, the insulation could be 50mm thick, and if the cables were covered by such that would satisfy the 50mm requirement.