I have a piece of industrial bakery machinery (bread moulder) where the stop button works shortly after starting the machine, but after say 30 seconds or so the Stop button no longer works.
The Emergency stop button works fine though.
It's a 24vDc control circuit.[ElectriciansForums.net] Wiring diagram assistance... [ElectriciansForums.net] Wiring diagram assistance...
So the Stop button itself checks out ok, and as I say it does work for the first 30 seconds or so of the machines operation.
Can't help but think I'm missing dome thing obvious....
[ElectriciansForums.net] Wiring diagram assistance...
 
It appears that once the machine is started and K1 and 1K1 ( motor contactor?) are both energised, when proximity sw S3 energises relay K3 the stop circuit is disabled.

Without knowing more it's difficult to understand what is going on.
 
As Andy points out according to the wiring diagram the stop button is looped out when both 1K1 and K3 are energised, having limited info and no specific key for the wiring plans then I can't comment too much further as I would need to know the full operation of machine and any sequence of events that occur to better understand why the Stop is been over-ridden by design.
 

Reply to Wiring diagram assistance... in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
787

Similar threads

  • Question
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...
Replies
14
Views
1K
  • Question
I would agree that the motor is by far the best part to replace. if it is powered and not turning then it is broken. Keep it simple!
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top