The specific model in the OP is the E213263 which is the CE marked variant and according the the specification it requires two phases (of a UK TP supply), neutral and Earth.

[ElectriciansForums.net] Wiring for 2ph coffee brewer
 
It looks as though it actually needs a 240v supply, not 400v, so looking at the diagram on the right, you would connect live to L1 and neutral to L2, the American system appears to be L1 to N is 120v, L1 to L2 is 240v. That's why the neutral is crossed out. I don't think it needs a 2 phase supply at 400v. Anybody else think that too??

You can see from the data plate in the OP that it is clearly a 230V/400V model, not a US 120V model.
The diagram you are referring to is for the US model (and other countries), the clue is in it being for 120V and 208-240V connections when the data plate on the OPs machine shows that it is a 230/400V model.
 
You can see from the data plate in the OP that it is clearly a 230V/400V model, not a US 120V model.
The diagram you are referring to is for the US model (and other countries), the clue is in it being for 120V and 208-240V connections when the data plate on the OPs machine shows that it is a 230/400V model.
Yeah I can see now the OP pic of label on box and the diagram are conflicting! I thought the OP put on the diagram after.
 

Reply to Wiring for 2ph coffee brewer in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
546
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
990
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
921

Similar threads

  • Question
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...
Replies
14
Views
2K
In July I moved into my new home with Schluter DITRA heated floors in the bathroom. The floor quit working in December, and my GC and a rep from...
Replies
0
Views
737

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top