Hi folks - some advice please! I am about to start fitting a new kitchen into our house here in Bulgaria and will be fitting new electric cable. The room is 3 metre square and I want to fit 3 double sockets on one wall and 4 double sockets on 2 of the other 3 walls (2 per wall) above the working surfaces plus 2 under the counter sockets for the fridge and dishwasher. There will also be 2 wall mounted switches for the cooker and extractor fan. 2 walls face the outside and are to be plasterboarded and insulated. The new cable will be running along the ceiling which is made from reinforced concrete slabs.The ceiling will also be plasterboarded after the cables are fitted. There will be a seperate cable for the cooker. The house is wired 3 phase.

Q1. Ring main or radial (1 radial or 2) 2.5mm.
Q2. Should the cable be in conduit or just clipped to the ceiling.
Q3. 6mm cable for the cooker?

Any other advice would be most welcome. Cheers, Steve
 
Q1. Ring main or radial (1 radial or 2) 2.5mm. ring is preferable
Q2. Should the cable be in conduit or just clipped to the ceiling. or clipped to walls just above/below platerboard ceiling.
Q3. 6mm cable for the cooker? upto 15kW, 6mm clipped direct on a 32A MCB will usually suffice.

20A D/P switches above worktop for the under worktop sockets and FCU for extractor fan advisable.

above subject to any Bulgarian regulations that may be different to ours here in the UK.
 
Did you know, Bulgarians make the best yoghurt in the world (allegedly), nod they heads up & down to say no & horizontally to say yes and they also play the bagpipes. Don't think they're into ring mains, sorry sorry sorry ring final circuits. :)
 
Did you know, Bulgarians make the best yoghurt in the world (allegedly), nod they heads up & down to say no & horizontally to say yes and they also play the bagpipes. Don't think they're into ring mains, sorry sorry sorry ring final circuits. :)
can't comment on the monkey snot (yoghurt) as i hate the stuff. bagpipes are only for the Bad Piper, and as for ring finals, choice is down to the installer/
 
Q1. Ring main or radial (1 radial or 2) 2.5mm. ring is preferable
Q2. Should the cable be in conduit or just clipped to the ceiling. or clipped to walls just above/below platerboard ceiling.
Q3. 6mm cable for the cooker? upto 15kW, 6mm clipped direct on a 32A MCB will usually suffice.

20A D/P switches above worktop for the under worktop sockets and FCU for extractor fan advisable.

above subject to any Bulgarian regulations that may be different to ours here in the UK.
Many thanks for your reply. Cheers - Steve
 
Do what you like it is bound to exceed their requirements.
Can't agree - a ring final circuit is likely to be a prohibited arrangement. There are also likely to be requirements which don't exist under BS 7671. There is a duty to ensure that any work satisfies their national requirements.
 
I have a Bulgarian chap on my course at the moment. I could ask him to pop round but I think he's committed in London at the moment. ;) Good luck Steve and welcome to the forum.
 
As far as I know in Bulgaria they use a shared neutral/cpc, hence only use two conductors, even in final circuits. I remember seeing a link between cpc and neutral inside a socket outlet when I was there a few years back.

Edit: And definitely no ring finals allowed!
 
As far as I know in Bulgaria they use a shared neutral/cpc, hence only use two conductors, even in final circuits. I remember seeing a link between cpc and neutral inside a socket outlet when I was there a few years back.

Edit: And definitely no ring finals allowed!
Yes, you are right. The earth and neutral are wired together in the socket outlet. Found this out to my cost soon after we bought the house (2003) when I pluged in a plastic pipe welder. Got a hell of a belt when I touched the metal housing of the welder. Some "bright spark??" had joined the live to the earth in the socket!! As far as I can tell ring finals are not used. So I rekon on splitting the sockets by using 2 radials.

Thanks to all who have commented. Cheers, Steve
 
Last edited:

Reply to Wiring for a new kitchen in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
273
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
267
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K
  • Question
ok cheers for the help lads
Replies
7
Views
677

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top