Wiring for Hob and Oven | Page 2 | on ElectriciansForums
Discuss Wiring for Hob and Oven in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Ezzekiel
I have an Oven Hob to install as posted, the oven as a cable attached but requires minimum 15Amp fuse, in this instance what would you advise as a standard 3 pin plug only has a 13 map fuse ??
My installation is a cooker outlet with 6 mm cable to outlet box.
if the min size is 15a wire it directly to the outlet plate (circuit sizing calcs as per usual)
circuit exceeding 15a but not exceeding 50a may serve upto two appliances in one room Osg
Reply to Wiring for Hob and Oven in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Terminal box on a UK cooker from 50 years ago would easily accomodate a 10mm2 cable, even though 6mm 2 was adequate. Nowadays, most cookers, ovens...
allowing for diversity a 32 amp supply will be fine for them both, but remember, the cable needs to be adequate to cope with a load on up to that...